The section on diversity in the OSG, has been the same content for quite some time, and is not reflective in modern appliances. So that guidance for RFC, can be taken with a pinch of salt. Unless your plugging in electric heaters in every socket outlet. Lighting circuits with LED lamps, will be only a few amps, again unless its like Blackpool illuminations. Get a clamp meter & check it out for yourself.
 
House+garage+workshop:
Starting with 7.4Kw Induction Hob (1st 10A plus 30% of the remainder) 16.6A already...
3Kw Immersion heater - No Diversity allowed another 13A...
3Ring + 3 Radial Circuits (100% of 1st & 40% of rest) 32+49.6 = 81.6A
+ 4 x 6A lighting - haven't worked out all the lights I'm having yet, so lighting diversity still up in the air (although mostly a mix of compact flourescents & LEDs).
I know diversity is a bit of a black art so any constructive comments/suggestions welcomed. As the immersion is only used in emergencies if CH not working. I'm wondering if there are any options there.
P.S I don't have a clamp meter yet.

Re the Hob (and the Oven if electric) won't necessarily draw their full current loads even when on max due to them being thermostatically controlled. Same goes for the immersion heater....
 
There’s little chance those ring circuits are going to pull over 80 amps after diversity, why not have a 20a radial upstairs, 20a radial downstairs and a ring for kitchen?
What are other radial circuits,
Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
I doubt very much your ever going to come anywhere near this.
I would recalculate put in an 80a kmf
 
There’s little chance those ring circuits are going to pull over 80 amps after diversity, why not have a 20a radial upstairs, 20a radial downstairs and a ring for kitchen?
What are other radial circuits,
Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
I doubt very much your ever going to come anywhere near this.
I would recalculate put in an 80a kmf
Radials are sockets in Garage, workshop & new utility room. Upstairs & downstairs are existing rings - don't really want to add work by converting to radials if I can avoid. Splitting kitchen off downstairs ring onto its own.
 
If you consider loads over 1kW, which could over a period of say an hour be on at the same time, some of which are thermostatically/simmerstat cycling on/off or controlled by a programmer, then I reckon your short-lived peak demand is:

Ind Hob 7kW (to take account of Christmas Day type useage)

Imm Htr 3kW

Wash Mach 2kW

Tumb Dry 2.5kW

Dish Wash 2kW

Electric Convection Oven 2.5kW

Total = 19kW = 79A at 240V for which 16mm2 tails and 60A/80A BS88 cut out is perfectly adequate.

Most of the time the load will be far less - I'd estimate the time-averaged power consumption over an hour period to be:

Ind Hob 2kW

Imm Htr 3kW

Wash Mach 0.5kW

Tumb Dry 1.5kW

Dish Wash 0.5kW

Electric Convection Oven 0.5kW

Total 8kW or circa 35A again well within the capacity of a 60A/80A BS88 fuse and 16mm2 tails.

In my home I have 2 TDs, 2WMs, DW, IH, 2 electric convection ovens all supplied by a 80A BS88. The short DNO meter tails are 16mm2 and the CU tails are 25mm2 but 16mm2 would have sufficed.
 
Completely agree with what Marconi has said, I can’t ever see the house pulling more than about 40 amps.

On your method though, your looking at it from the wrong angle if you have a down ring which is ok, why do you need to split it as this is adding another 14 or so Amps to your calc for an extra ring circuit
 
House+garage+workshop:
Starting with 7.4Kw Induction Hob (1st 10A plus 30% of the remainder) 16.6A already...
3Kw Immersion heater - No Diversity allowed another 13A...
3Ring + 3 Radial Circuits (100% of 1st & 40% of rest) 32+49.6 = 81.6A
+ 4 x 6A lighting - haven't worked out all the lights I'm having yet, so lighting diversity still up in the air (although mostly a mix of compact flourescents & LEDs).
I know diversity is a bit of a black art so any constructive comments/suggestions welcomed. As the immersion is only used in emergencies if CH not working. I'm wondering if there are any options there.
P.S I don't have a clamp meter yet.

If the immersion is only a backup then ignore it for this purpose.

81.6A of portable/small appliances in a house sounds ridiculous to me, does the total running current of every appliance you own actually add up to that much?

It helps to actually think about the real world rather than getting lost in the numbers written in a book.
What will actually be plugged in and operating during the average day, and will it all be on at the same time?
 
Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
/QUOTE]
Thanks for that. Fig 3A1(page 319) is most illuminating. Few discussions of diversity refer directly to this time factor and its clearly very relevant.
 
Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
Thanks for that. Fig 3A1(page 319) is most illuminating. Few discussions of diversity refer directly to this time factor and its clearly very relevant.
 
Last edited:
PPP

Post pictures please
TailsfromMeterBox (Large).jpg

TailRoute (Large).jpg
 
That is a bit of a lash up, what you want is a bit of swa cable :rolleyes:

Could the tails be routed out the back of the meter box, then surface inside in some plastic trunking?
 
If it's SWA why would I use surface trunking? The problem I'm facing really, is once it reaches the porch getting it through the brickwork and wooden beam to the void. Ironically the supply to the meter appears to originate from somewhere under the concrete floor inside the porch, but moving the meter inside isn't really an option.
 
If it's SWA why would I use surface trunking? The problem I'm facing really, is once it reaches the porch getting it through the brickwork and wooden beam to the void. Ironically the supply to the meter appears to originate from somewhere under the concrete floor inside the porch, but moving the meter inside isn't really an option.

Trunking looks a little nicer than cleated SWA.

To get through the brickwork and wood drill a hole.

It’s not really ironic, it’s just probably been moved outside from it’s original location inside.
 
Really ? Please refer to previous comments of concern suggesting you get an electrician in.
I am involving another electrician... As mentioned previously. Existing tails are in plastic conduit embedded in the wall. This is more like passing through the wall in conduit as does the DNO supply.
If you have feedback on the method based on standards, please refer.
 
Really ? Please refer to previous comments of concern suggesting you get an electrician in.
I am involving another electrician... As mentioned previously. Existing tails are in plastic conduit embedded in the wall. This is more like passing through the wall in conduit as does the DNO supply.
If you have feedback on the method based on standards, please refer.
 
I am involving another electrician... As mentioned previously. Existing tails are in plastic conduit embedded in the wall. This is more like passing through the wall in conduit as does the DNO supply.
If you have feedback on the method based on standards, please refer.
If another electrician is involved then it would be most appropriate to ask them about installation methods and all other aspects of the installation if they are to be signing certificates. That is what I would expect if I were doing the same favour.
 
I am involving another electrician... As mentioned previously. Existing tails are in plastic conduit embedded in the wall. This is more like passing through the wall in conduit as does the DNO supply.
If you have feedback on the method based on standards, please refer.
So you have the help of two Sparkies then?
 
Not acceptable in my opinion, it would have to be earthed metal conduit to fully comply with the regulations.
I'm actually following the electricians instructions... but thanks for the heads up, I will raise it with him.
(For the benefit of anyone else trying to learn from this thread, the regulations we are discussing here are 522.6.x)
I'm now leaning back towards using 25mm SWA (2 core as I already have a decent earth) with a Henley block once I reach the void (more than 50mm deep) to convert back to double insulated tails and minimise issues with bend radius.
 
I'm actually following the electricians instructions... but thanks for the heads up, I will raise it with him.
(For the benefit of anyone else trying to learn from this thread, the regulations we are discussing here are 522.6.x)
I'm now leaning back towards using 25mm SWA (2 core as I already have a decent earth) with a Henley block once I reach the void (more than 50mm deep) to convert back to double insulated tails and minimise issues with bend radius.
How will you provide an earth for the armouring on the SWA 2 core?
 
From looking at the photo's could you not just box that part in therefore you could use standard 25mm tails further back than 50mm outside run in plastic trunking (could even semi recess into pebbledash).
 
Good point thank you, my thinking hadn't got that far. I could maybe gland off to a galvanised conduit angle box and use Pratley box connectors instead of the Henley block. Plenty of earth's available in the void I could use.
I could use a Pratley box for that matter but seems an expensive option and a bit overkill.
Other than that I would have to put the Henley block in some other sort of box that I could gland off to.
 
From looking at the photo's could you not just box that part in therefore you could use standard 25mm tails further back than 50mm outside run in plastic trunking (could even semi recess into pebbledash).
The bit I am putting in the wall is in the middle between the void and the outside wall, so I don't quite follow you. If you are suggesting I run it on the surface inside the house, yes I could probably do that, but a bit of a cop out as would be rather unsightly.
 
The bit I am putting in the wall is in the middle between the void and the outside wall, so I don't quite follow you. If you are suggesting I run it on the surface inside the house, yes I could probably do that, but a bit of a cop out as would be rather unsightly.
From looking at the photo would be only bringing the wall level with the door.
 

Reply to SWA For meter tails? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
885
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock