Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
/QUOTE]
Thanks for that. Fig 3A1(page 319) is most illuminating. Few discussions of diversity refer directly to this time factor and its clearly very relevant.
 
Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
Thanks for that. Fig 3A1(page 319) is most illuminating. Few discussions of diversity refer directly to this time factor and its clearly very relevant.
 
Last edited:
PPP

Post pictures please
TailsfromMeterBox (Large).jpg

TailRoute (Large).jpg
 
  • Like
Reactions: Rpa07
That is a bit of a lash up, what you want is a bit of swa cable :rolleyes:

Could the tails be routed out the back of the meter box, then surface inside in some plastic trunking?
 
That is a bit of a lash up, what you want is a bit of saw cable :rolleyes:

Could the tails be routed out the back of the meter box, then surface inside in some plastic trunking?
saw cable?
 
I would consider using a 16mm split concentric chopped in the wall Covered by an earthed 3mmsteel plate covering, from the incomer connected to a kmf isolator
 
If it's SWA why would I use surface trunking? The problem I'm facing really, is once it reaches the porch getting it through the brickwork and wooden beam to the void. Ironically the supply to the meter appears to originate from somewhere under the concrete floor inside the porch, but moving the meter inside isn't really an option.
 
If it's SWA why would I use surface trunking? The problem I'm facing really, is once it reaches the porch getting it through the brickwork and wooden beam to the void. Ironically the supply to the meter appears to originate from somewhere under the concrete floor inside the porch, but moving the meter inside isn't really an option.

Trunking looks a little nicer than cleated SWA.

To get through the brickwork and wood drill a hole.

It’s not really ironic, it’s just probably been moved outside from it’s original location inside.
 
  • Like
Reactions: Rpa07
  • Friendly
Reactions: MickK
I was suggesting an alternate to swa, some 6181y and surface plastic trunking?
OK. Yes, looks like this is the way I'm going to go, then straight through the wall and cut a channel round the outside of the brick pillar (inside the porch), through into the void.
 
OK. Yes, looks like this is the way I'm going to go, then straight through the wall and cut a channel round the outside of the brick pillar (inside the porch), through into the void.

When you say cut a channel you don’t mean to bury the tails in the wall do you? Because then they’d need RCD protection which would be unacceptable.
 
When you say cut a channel you don’t mean to bury the tails in the wall do you? Because then they’d need RCD protection which would be unacceptable.
In conduit.
 
When you say cut a channel you don’t mean to bury the tails in the wall do you? Because then they’d need RCD protection which would be unacceptable.
In conduit.
 
Really ? Please refer to previous comments of concern suggesting you get an electrician in.
I am involving another electrician... As mentioned previously. Existing tails are in plastic conduit embedded in the wall. This is more like passing through the wall in conduit as does the DNO supply.
If you have feedback on the method based on standards, please refer.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Msitekkie

Arms
~
Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)