timhoward
Broke Internet
Supporter
Jul 19, 2019
4,629
9,864
18,688
Oswestry
Just double checking please - in situations where the main earthing conductor csa is calculated, and in a TNS installation, the 50% bonding conductor csa rule still applies to your final calculated and rounded up earthing conductor size? (As opposed to the tabulated size)
I'm doing remedials and someone else gave a C2 for the main earthing only being 6mm csa as line conductors are 16mm, and also gave C2 and said the 6mm csa main bonding should be 10mm. It is very definitely TNS.
However the formula confirms that in fact 6mm earthing is fine (it's a sub main with C32 breaker protecting it and low PFC), and as long as the 50% is based on the 6mm I can't see why the main bonding is an issue either.
So it's a cpc not an earthing conductor?
So the main protective bonds are located at the end of this submain and supported by the 6.0 cpc.
Reactions: timhoward
In fact more complex. Looked more closely now.
16.0 cpc as far as adaptable box (one core of SWA). 16.0 cpc to an MET block. 10.0 cpc from MET to CU.
Bonding conductors to gas, water are 6.0
timhoward
Broke Internet
Supporter
Oswestry
Main Bonding csa when earthing csa calculated
timhoward,
timhoward,