Just double checking please - in situations where the main earthing conductor csa is calculated, and in a TNS installation, the 50% bonding conductor csa rule still applies to your final calculated and rounded up earthing conductor size? (As opposed to the tabulated size)
I'm doing remedials and someone else gave a C2 for the main earthing only being 6mm csa as line conductors are 16mm, and also gave C2 and said the 6mm csa main bonding should be 10mm. It is very definitely TNS.
However the formula confirms that in fact 6mm earthing is fine (it's a sub main with C32 breaker protecting it and low PFC), and as long as the 50% is based on the 6mm I can't see why the main bonding is an issue either.
 
So it's a cpc not an earthing conductor?
 
So the main protective bonds are located at the end of this submain and supported by the 6.0 cpc.
 
  • Like
Reactions: timhoward
In fact more complex. Looked more closely now.
16.0 cpc as far as adaptable box (one core of SWA). 16.0 cpc to an MET block. 10.0 cpc from MET to CU.
Bonding conductors to gas, water are 6.0
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

timhoward

Broke Internet
Esteemed
Arms
Supporter
~
Joined
Location
Oswestry

Thread Information

Title
Main Bonding csa when earthing csa calculated
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
timhoward,
Last reply from
timhoward,
Replies
4
Views
1,754

Advert