Just found this on another forum… no comments on the actual pic…this can’t be right can it?
8999A504-C72F-4AF2-AE51-B36668356333.jpeg
 
Last edited by a moderator:
  • Like
Reactions: James
Just found this on another forum… no comments on the actual pic…this can’t be right can it?
In what way can't it be right Mate
 
Taking the single cores through separate holes like that is a big no, no.
assuming of course that the base of the enclosure is steel and that no other provisions have been made to prevent eddy currents.
 
Taking the single cores through separate holes like that is a big no, no.
assuming of course that the base of the enclosure is steel and that no other provisions have been made to prevent eddy currents.
Agree with you ,but we have no other information, just a picture of an isolator with singles entering at the bottom.
Is the base plate ferrous? if so has it been slotted in line with best practice? for all we know the cable eateries may have been made in an insulating material, no info on that from the poster
 
No one commented on it …to me it don’t look right…obviously the entries into the isolator..definitely metal enclosure.
 
  • Like
Reactions: James
Would be interesting to see what the removable bottom entry plate looks like:

1631434682373.png
 
  • Like
Reactions: DPG and nicebutdim
No one commented on it …to me it don’t look right…obviously the entries into the isolator..definitely metal enclosure.
No problem if it's a metal enclosure, it's the entry plate that causes problems with eddy currents
 
  • Agree
Reactions: James
Question is.... what are you doing on another forum?
Traitor!

?
 
Just found this on another forum… no comments on the actual pic…this can’t be right can it?
Well I can't see where the metal enclosure is earthed??

But without a picture of the entry plate it is hard to tell whether the tails have been correctly installed to prevent eddy currents
 
  • Like
Reactions: loz2754
Well I can't see where the metal enclosure is earthed??

But without a picture of the entry plate it is hard to tell whether the tails have been correctly installed to prevent eddy currents
Copper sheath of the MICC????
 
Agree that it's impossible to tell whether it's OK or not. If there is a slot between the holes or the plate is non-ferrous, it's fine. If not, it's not, although currents of this order (63A) through unconnected holes in a mild steel gland plate do not usually cause any significant issues in practice.
 
  • Like
Reactions: DPG
Where is the MICC you speak of!!!
The 4 cables entering the all metal enclosure! at the lower elevation.
 
Edit my last after a better look the cables are tails PVC/PVC Singles, sorry for confusion
 
Edit my last after a better look the cables are tails PVC/PVC Singles, sorry for confusion
So where is the enclosure earthed!!
 
  • Like
Reactions: DPG
So where is the enclosure earthed!!
How long is a bit of string mate, your guess is as good as mine, but vwe aint talking earthing it's eddy currents we are yapin about
 
I found this video re domestic sized installations quite informative:

 
Hello to all,

Rather than start another eddy current thread, thought I'd just tag onto this one.

Cables contained in metal trunking which is bushed to the side of a 12TP dis board. Lives and neutrals go through one 50mm brass Bush into RCBOs. The earths go through another 50mm hole which is in line with the earth bar.

Will the brass bushes prevent eddy currents as the brass isn't magnetic?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Eddy
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
cliffed,
Last reply from
James,
Replies
27
Views
3,951

Advert