OK, so you just need to meet the SWA fault protection so RCD up-front on basically any SWA choice, and a rod arrangement below 200 ohms. What is the surrounding soil/ground like?
Haven't had a dig yet but I've been looking at bentonite if I'm struggling for a good reading.
 
Hi all, looking for a bit of advice and confirmation on my proposed plans for a SWA sub main to a ISO metal storage container. I've calculated the max demand in the ISO will be about 20A (300w of led lighting and 2 double sockets for chargers etc) It will be fed from a 3ph DB in another building. The cable run is 100 meters, I'm planning on using 16mm 2 core swa ( Volt drop calcs allow about 35A with 16mm) and installing a rod at the container (the vast majority of the cable run is at height, clipped to the building). The container will have a small 4 way board with RCD main switch.
The 16mm will be fed from a C32 breaker in the 3Ph board. Im installing double insulated 16mm tails and a 16mm earth from the 3ph DB to a meter (needs a meter installed) then from the meter to an adaptable box where I will terminate the SWA. Due to the fact that I'm using a rod at the other end, I'm planning on a 100ma S rcd for fault protection for the SWA (inside the adaptable box).
Can anybody see any glaring errors in my method? I have spoke to Napit and they were fine about my proposed plan, but they didn't mention the 100mA rcd.
Thanks in advance!
I take it the Earthing System for the upstream supply is a TN-C-S???
 
Haven't had a dig yet but I've been looking at bentonite if I'm struggling for a good reading.
Clay cat litter is cheaper and the same sort of stuff!

Obviously check for any buried services as far as you can. There are sites like this for main stream power & gas, but not everyone is on there:

Also remember that the main factor is soil conductivity is moisture, so if you can go deeper (say 8' = 2.4m rod, typically in two sections) you will generally do better than two short ones in parallel as more chance of the soil remaining moist.

I have used M16 stainless studding as an earth rod driven in like a giant drill (SDS adaptor and a 1/2" drive stud runner), but obviously you get purpose made ones and matching bit like access boxes, etc. For example:
 
  • Like
Reactions: TheCodboy
Clay cat litter is cheaper and the same sort of stuff!

Obviously check for any buried services as far as you can. There are sites like this for main stream power & gas, but not everyone is on there:

Also remember that the main factor is soil conductivity is moisture, so if you can go deeper (say 8' = 2.4m rod, typically in two sections) you will generally do better than two short ones in parallel as more chance of the soil remaining moist.

I have used M16 stainless studding as an earth rod driven in like a giant drill (SDS adaptor and a 1/2" drive stud runner), but obviously you get purpose made ones and matching bit like access boxes, etc. For example:
Just did a job today where a house had no main earth. Did a Zs at the sockets and it was 290 Ohms. Did as bit of digging out, probably a couple of feet and got the 4ft rod pretty much all the way in. Ze of 28 ohms. That'll do for me!
 
  • Like
Reactions: BenCos18 and pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

TheCodboy

Arms
~
Joined
Location
Newcastle

Thread Information

Title
SWA Sub Main advice/comments
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
TheCodboy,
Last reply from
TheCodboy,
Replies
23
Views
3,670

Advert