Mar 7, 2023
28
Sheffield
Trainee Electrician
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right protective devices for :
A 32A distribution circuit from the main board to supply summerhouse will have a four-way SP-N distribution board fitted supplied by a 3-core thermoplastic SWA cable clipped direct. In the main board all the other circuits are on RCBOs.
I'm pretty sure I can't have a RCBO feeding another RCBO because of discrimination , and I think because the supply is wired in SWA that the distribution circuit doesn't need RCD protection .If I am correct in thinking this could someone give me the reason to why the circuit being wired in SWA means no rcd protection is needed
What I have done for this question is a 32A MCB in the main board for this distribution circuit feeding the summerhouse board and in the summerhouse I have put RCBOs in that four-way board- Is this correct ?
I also had another thought that I could do a 32A RCBO in the main board for this distribution circuit feeding the summerhouse board and then have just MCBs in the 4 way - board
I am quite confused about this and have been looking through section 5 of the regs but the words and the way the regs describe things don't make things crystal clear to me
Reactions: timhoward
You have the right idea.
The basic thinking is
"Do I need an RCD for fault protection"
"Do I need an RCD due to the circuit's use (e.g. 411.3.3 411.3.4, or any of the section 7 special location rules"
"Do I need an RCD due to the wiring system and how the cable is run"
The last one is the one of interest here - and the journey goes:
Section 5 - selection and erection of equipment
Section 52 - " " wiring systems
Section 522 - " " in relation to external influences
finally arriving at section 522.6 Impact
If you read through that bit, remembering that SWA has an earthed metallic covering, you'll see the reason why your hunch is right.
If still confused feel free to fire questions back.
so the circuit is protected by the earthed metallic covering in the armoured cable
What is the earthing system at the house ?
What is the size of the swa?
Is there any extraneous conductive ?
I could just say "yes", but the definition of protected is a little ambiguous.
I know this sounds daft but you don't need an RCD unless you need one!
So thinking about fault protection (will it turn off under fault conditions) - as long as the Zs is under the limit for the protective device, the answer is yes. So if it's a B32 breaker, Zs of less than 1.1 ohms (on site guide value). If it isn't (e.g. the earthing system is TT) then you will need an RCD to meet disconnection times.
It isn't any of the things that the regs say need RCD protection (e.g. a final circuit for sockets, domestic lighting,) or a special location so no rules there apply.
The final consideration is Impact Protection. This section of the regs is one of the most confusing to wade through but it probably doesn't meet the criteria for 201, 202 or 203 and in any case you meet the "or else" 204 rule as it has an earthed metalic covering.
Reactions: WilliamAtkin
its a college project - TN-C-S system
there is no info in the spec on what size SWA and there isn't enough info to work it out (i don't have any info on the ambient temp or grouping factors like I did for other circuits ) and in the cable calculations part of the project I wasn't ask to work out the cable size of this circuit but i would assume a 2.5mm or 4mm swa would be used
there is no info in the spec about extraneous conductive
but yh I am going to stick with my initial design of an mcb from main board in hotel to feed the summerhouse which will have rcbos
and I have just noticed that quote at the bottom of what you wrote saying “Why would a spark do something so stupid”
And 1st of all I'm not a spark yet I am an apprentice in my 2nd year at college and prior to starting my apprenticeship I had no experience with electrics at all . Furthermore its rude to make a comment like that when I was just asking for help on this forum
Reactions: davesparks
thank you I think I got my head wrapped round it in the end
Easy - that’s his signature that appears on every post - it refers to a YouTube video by Delroy (eastway electrical) that a lot of us have seen.
So it wasn’t a personal comment aimed at you.
  • Friendly
Reactions: pc1966 and DPG
Oh ok that makes sense my bad I'm new to this forum and I just read that at the bottom and thought it was directed to me
And in the final bit of my project of this part is to pick protective devices for the hotel block.
There isn't that much info on the hotel block but the info I have been provided with is as follows: "The existing hotel building forms part of an 400V three-phase TN-C-S system...A new CCU will be installed to supply the distribution circuits. Ze is 0.09 and PFC is 5kA" - There are 8 distribution circuits to feed 8 sub boards, each board then feeds 2 rooms- each room has 1 socket circuit , 1 air con supply and I'm assuming one lighting circuit although the spec hasn't stated it. There is no information on what cables will be used and how they will be installed(as with the café block in this project I was provided with this info).I was going to use RCBOs in the sub board and then 3 pole MCBs to supply the sub boards and I'm confused to whether these distribution circuits need RCD protection. If they do need RCD protection then I will put a 100ma RCD to protect these distribution circuits as I know I would need the 3:1 ratio with the other RCD devices(RCBOs in sub boards) and the RCBOs in the sub boards are going to be rated 30mA so if a fault happens in any of the circuits in the sub boards it then doesn't trip the RCD protecting the distribution circuits. But if no RCD protection is needed for these distribution circuits then I will just have the 3 pole MCBs on their own. Am I right in thinking this ?
MCB's are rarely suitable for protection of distribution circuits as they don't afford much selectivity with the downstream devices.
Generally it is better to protect distribution circuits with MCCBs or fuses.
If they do need RCD protection then a 100mA device may not be suitable.
Also, for selectivity consider time delayed devices rather than 100mA devices.
Note, I'm not saying any of this is required in this case though. Do your SWA sub mains need RCD protection?
If I've got this right there's 3ph supply to main db, then 8 distribution circuits to boards that each serve two rooms. Rooms have an aircon unit, socket and lighting.
Given that selection of materials will be a factor in any college assignment, I can't help wondering why 3 pole MCBs are being considered for protection of distribution circuits?
Tbh with you I only work in domestic premises and I have never come across any 3 phase installations at work so I generally don't know. I thought that for 3 phase circuits you would need a 3 pole circuit breaker and due to discrimination I didn't think I could have a rcbo feeding an rcbo but idk I'm finding this quite confusing
I don't know if they are SWA in the hotel area as no info is given
On a separate board in the café block I had one distribution circuit to a summerhouse which was stated as SWA
But for these distribution circuits there is no info on how they are installed and what cable type- I think I'm just meant to select the correct protective devices for the sub boards and distribution circuits so that they are eligible
It does seem like maybe a little more info should have been given you.
Reactions: nicebutdim
If I'm reading it right you have a 3ph distribution board, 8 distribution circuits, and 8 single phase boards.
i.e. there is nothing that needs 3 phase for the pair of hotel rooms?
If so you can pretty much consider the 3 phase board as you would a single phase board, it just happens to be the case that every protective device will be using any one of the three phases.
Do you have plans or a means of working out the distance of the cable runs?
If you are then you should be able to work backwards working out the max demand of a pair of rooms, choose a likely cable size that can carry this, calculate the Zs for that cable size and the length, and then calculate the volt drop. If all that comes out ok for a given cable size then you won't need RCD protection to achieve fault protection.
Better answer from Tim than I could have given.
Without knowing full details of the project I don't want to lead you in a wrong direction, but everything points to 8 single phase circuits.
Would these MCCBs need RCD protection ?
Same issue as for MCB or fuse design - it depends on the end of circuit Zs being acceptable to meet distribution circuit disconnection times (typically 5s for TN systems) for the chosen OCPD, and assuming SWA or similar cable so no need for RCD "additional protection" against shock on cable damage.
It’s obviously frustrating NOT to be issued with enough information for your paperwork test scenario.! But that’s probably as it’s not what their look for from you.
Start thinking about different value types of RCBOs ??? What does that ‘Letter’ before the amp rated number mean. or B32 C32 D32.
That's still going to be dependent on cable type or installation method.
Sheffield
Trainee Electrician
Does a 32amp distribution circuit wired in SWA to a sub board need RCD protection ?
WilliamAtkin,
timhoward,