I wanted to convert 5 halogen down lights with new LED fittings and got these from TLC https://www.tlc-direct.co.uk/Products/CLH2CSPW.htm together with a Varilight V-COM as per recommendations.
Installed it all but the LEDs would not light up - even though I programmed the switch with 3 ON/OFF presses etc etc etc.
I then removed one LED and replaced it with one old halogen fitting. The dimmer controlled that one halogen fine but none of the LEDs.

Any suggestions on what I should try next?
 
Last edited:
Welcome to the black art of LED dimming. Only thing I can suggest is that these LEDs require trailing edge dimming, not leading.
 
What rating is the V-Com (VA/W)?
It sounds like you may need to set the boost limit higher - programming issue?
 
I specifically asked TLC-Direct as to which dimmer to use and they said V-Com
What rating is the V-Com (VA/W)?
It sounds like you may need to set the boost limit higher - programming issue?
The rating is 0 to 100W
 
Think you were ill advised by TLC, looks like it is the wrong dimmer, try the V-Pro dimmer.
 
The datasheet for the fitting states DM298FP, which is trailing edge.

Many thanks for the guidance. I just wonder why the TLC guy missed that.

As the dimmer I want is in a faceplate with two others, I reckon I will need the DM298GRID rather than DM298FP which is a single faceplate switch.
 
Many thanks for the guidance. I just wonder why the TLC guy missed that.
Because the staff at TLC are sellers of cardboard boxes, not electricians. There's a notice to that effect above most electrical wholesaler's trade counters.
 
  • Like
Reactions: Pretty Mouth
Many thanks for the guidance. I just wonder why the TLC guy missed that.
And maybe motivated by the fact TLC don't stock Colingwood dimmers, but they do V-COM/PRO 🤪
 
Last edited:
Doesn't have to be that Colingwood dimmer, but is does need to be trailing edge.
 
  • Like
Reactions: Avo Mk8
Installed it all but the LEDs would not light up - even though I programmed the switch with 3 ON/OFF presses etc etc etc.
I then removed one LED and replaced it with one old halogen fitting. The dimmer controlled that one halogen fine but none of the LEDs.
Hmmm, I would have expected some sign of life from these, even with an incompatible dimmer. Did the old halogen fittings take MR16 bulbs, or GU10? Just wondering if there's a 12V transformer hidden in the ceiling space somewhere.
 
. Did the old halogen fittings take MR16 bulbs, or GU10? Just wondering if there's a 12V transformer hidden in the ceiling space somewhere.
I thought of that, and discounted it because the OP said it worked with one of the old lamps back in, but reading the OP again, that actually proves nothing, so you may well be onto something.
 
The datasheet for the fitting states DM298FP, which is trailing edge.
Surprisingly, the instructions actually specify a Varilight V-Com dimmer as suitable
 
I thought of that, and discounted it because the OP said it worked with one of the old lamps back in, but reading the OP again, that actually proves nothing, so you may well be onto something.
I read that as 'only the halogen lit up' but you could be right. @Tomdhu , could you clarify please?
 
Hmmm, I would have expected some sign of life from these, even with an incompatible dimmer. Did the old halogen fittings take MR16 bulbs, or GU10? Just wondering if there's a 12V transformer hidden in the ceiling space somewhere.
Wow!! I reckon you cracked it.!
I just checked the old halogens and they are 12v MR16. What threw me was that wiring to each was grey T&E and when I pulled each one out, there was no sign of a transformer. Also, all the other downlights in the kitchen and hall were 230volt. It's late now so I will do some checks tomorrow with a multi meter just to double check.Much appreciated PM.
 
Back in the day, I used to fit MR16s in preference to GU10s, because of their greater efficiency, and generally fitted one transformer for every three lamps. I would place the transformers often some distance from the lamps, somewhere where they were accessible and away from insulation.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
LEDs not lighting with V-Com dimmer
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
15

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Tomdhu,
Last reply from
brianmoooore,
Replies
15
Views
727

Advert