If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Couldn't believe it the other day when we were having a quick walk around a guesthouse prior to an EICR scheduled for next week. Okay they weren't all electric, but 12 of them were! The property comprises of 11 ensuite bedrooms plus 3 bed owners accomodation and a small salon. Half of the showers were spread between 4 consumer units, the other 6(!!) came off another consumer unit, covered by one 80A RCD! Entire installation fed from a single 100A supply! We are talking nine 8.5kWs, two 9kWs and a 7kW (the other two were pumped), plus the sockets, lights, cooker, etc!

"And you've never had any nuisance tripping, etc?"
"nope, not in 8 years!"

Must be the luckiest man on Earth!
 
If I were doing an EICR on this property the first thing I would do is to take a look at the 100A main fuse to see if it has been linked out? Come across this a lot with older buildings that only has a 100A single phase supply and over the decades with more and more electrical appliances installed, (eg showers, cookers, loads of extra sockets, heaters etc) a cowboy spark or the owner will link out the main fuse so it does not trip. It also does not protect anything and is very dangerous.

Just to add a note just in case. If the main 100A bullet is in a red casing it will be linked out by design by the DNO. Believe it was used for isolation only with other BS1361 fuses up stream protecting the internal supply for each DB. Phil D (a member on here) was published in Professional Electrician magazine last year on this topic.
 
  • Like
Reactions: 1 person
Just to add to what Paul has put, remember the carrier if linked out you will need to find the maximum current it is designed to carry. Therefore you max demand may exceed that before you have started doing any inspection or testing.
 
  • Like
Reactions: 2 people
and then advise a 3 phase supply. £££££££££££££s
 
  • Like
Reactions: 1 person
@ Resu, please find out as much as you can when you and your gaffer go to this EICR next week and post up your findings. This is an interesting one. Think we would all like to know more about it and this is a great discussion for us all on how to resolve the problems you both find. Good thread.
 
  • Like
Reactions: 2 people
If I were doing an EICR on this property the first thing I would do is to take a look at the 100A main fuse to see if it has been linked out? Come across this a lot with older buildings that only has a 100A single phase supply and over the decades with more and more electrical appliances installed, (eg showers, cookers, loads of extra sockets, heaters etc) a cowboy spark or the owner will link out the main fuse so it does not trip. It also does not protect anything and is very dangerous.

out of interest chaps ....

if you notice something as dangerous as this in a house, what are you supposed to do?
 
Pray to Allah........it may not help, but I understand there are a few virgins init somewhere
 
  • Like
Reactions: 1 person
out of interest chaps ....

if you notice something as dangerous as this in a house, what are you supposed to do?

nick the lead off the roof and leggit.
 
Pray to Allah........it may not help, but I understand there are a few virgins init somewhere

No point ...

Virgins.png
 
  • Like
Reactions: 1 person
If I were doing an EICR on this property the first thing I would do is to take a look at the 100A main fuse to see if it has been linked out? Come across this a lot with older buildings that only has a 100A single phase supply and over the decades with more and more electrical appliances installed, (eg showers, cookers, loads of extra sockets, heaters etc) a cowboy spark or the owner will link out the main fuse so it does not trip. It also does not protect anything and is very dangerous.

Just to add a note just in case. If the main 100A bullet is in a red casing it will be linked out by design by the DNO. Believe it was used for isolation only with other BS1361 fuses up stream protecting the internal supply for each DB. Phil D (a member on here) was published in Professional Electrician magazine last year on this topic.

Interestingly enough the fuse was present and correct. I have seen the red casing fuse holders before inside a small blocks of council flats.

Not sure what we would really be able to do as we have already mentioned the potential issues to the client and we got "well it's been fine for the past eight years", so would likely be difficult to convince him to change it in any way, especially seeing it would cost a fair bit to sort it properly.

Out of interest, what would you do Paul? (or any of the other mentors for that matter?). Bit of a difficult one!

out of interest chaps ....

if you notice something as dangerous as this in a house, what are you supposed to do?

I wouldn't say it was dangerous as such mate, worst that is going to happen is the RCD would trip or the main fuse would blow, which is more inconvenient than anything else!
 
Right EICR complete today. A number of issues but relatively small stuff! Client has decided not to do anything about the shower situation despite our comments regarding slight overloading! Some of the issues we found:

2 showers fed from the same breaker!
3kW under sink water heater spurred from shower switch (fed from above breaker!)
2x 2.5mm radials protected by 32A breakers
Lighting circuit in extension - class 1 fittings, not earthed and no RCD protection

And the usual loose connections causing dodgy readings on the ring tests, why is it always the last one you check?!

And some other fun stuff. So a few remedials!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Resu

Mentor
Arms
~
Joined
Location
Scottish Highlands
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
14 Showers, one property
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Resu,
Last reply from
Resu,
Replies
11
Views
225

Advert