16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb

Discuss 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
19
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.

Cheers
 

Reply to 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net