Mike Watters
a 5 story house has 10 sub mains 16mm t+e feeding wylex consumer units in each of 10 rooms.each room has 1x 6amp lighting circuit, 1 x 32 amp radial and 1 x 32 amp cooker circuit. the cables were fitted about 10 years ago. the wylex boards 2 years ago. a periodic report says the 16mm dis circuits are inadequate and i was also told by a spark mate that the 6mm cpc in the 16mm dis cable is too small a csa. the dis cables are protected by 60 amp fuses. to test fully do i do the ze at the dis boards in the rooms or at the origin. do i zs test the dis cables 1st and then the final circuits after and do i add the results. i know 6 + 32 + 32 is greater than 60amps but i can put 20 amp breakers on the sockets circuit to stop overload. any help is great. thanks.