I am a student currently on 2365 level3 I am currently stuck on question 10 and needed some guidance. I have filled in what I could not sure if it is correct.
 
P

pc1966

Esteemed
Arms
Reaction score
5,982
Some hints - there is always one isolation switch for electrical maintance in any complaint house installation, where is it likely to be?

Also don't see "mechanical maintenance" in the strictest sense such as in terms of a factory. Can you think of fixed wired household items that have local switches you might use before, say, trying to clean inside them?
 
E
Reaction score
0
View attachment 58591
I am a student currently on 2365 level3 I am currently stuck on question 10 and needed some guidance. I have filled in what I could not sure if it is correct.
This question may be answered using the Table 1 or Table 2. It is strongly recommended that you use

pencil when completing the table to allow for recalculation of figures.



Determine, for every final circuit in the café/pool block, each of the following.

a) Design current (Ib)

b) Nominal rating and type of protective device (In)

c) Method of installation reference

d) Rating factors that apply

e) Minimum cross-sectional area of live conductors for current capacity and voltage drop

f) Actual voltage drop.

g) Maximum permissible disconnection time for each circuit as given in BS 7671.

h) Earth fault loop impedance

i) Maximum earth fault loop impedance as stated in BS 7671.

Hi have you done this question? I'm currently working on but having trouble with it
 
OP
H

haroonmahmood

Trainee
Reaction score
4
This question may be answered using the Table 1 or Table 2. It is strongly recommended that you use

pencil when completing the table to allow for recalculation of figures.



Determine, for every final circuit in the café/pool block, each of the following.

a) Design current (Ib)

b) Nominal rating and type of protective device (In)

c) Method of installation reference

d) Rating factors that apply

e) Minimum cross-sectional area of live conductors for current capacity and voltage drop

f) Actual voltage drop.

g) Maximum permissible disconnection time for each circuit as given in BS 7671.

h) Earth fault loop impedance

i) Maximum earth fault loop impedance as stated in BS 7671.

Hi have you done this question? I'm currently working on but having trouble with it
This question may be answered using the Table 1 or Table 2. It is strongly recommended that you use

pencil when completing the table to allow for recalculation of figures.



Determine, for every final circuit in the café/pool block, each of the following.

a) Design current (Ib)

b) Nominal rating and type of protective device (In)

c) Method of installation reference

d) Rating factors that apply

e) Minimum cross-sectional area of live conductors for current capacity and voltage drop

f) Actual voltage drop.

g) Maximum permissible disconnection time for each circuit as given in BS 7671.

h) Earth fault loop impedance

i) Maximum earth fault loop impedance as stated in BS 7671.

Hi have you done this question? I'm currently working on but having trouble with it

I have not completed but done part of the question as I also need help on this. my college will be reopening in 2 weeks so I will be continuing once I speak to my lecturer.

a) you work out the design current for every circuit. for me I have 11 lighting circuits.
what I did was calculate the total power of each lighting circuit and divide it by the voltage of 230v for each circuit which gives you the 𝐼𝑏.

Example- Circuit1- Has 3 lights total power of them 3 lights was 62w
𝐼𝑏= 𝑃𝑜𝑤𝑒𝑟/voltage = 62/230=0.27A

you have to do this for all of your circuits.

b) you have to choose Select 𝐼𝑛 which should be equal to or greater then Ib which basically means a protective device to protect each one of your circuits but has to be equal to or greater then the design current you which you calculated in a) for each circuit.
I had chosen a rcbo of 6A tybeB breaker as it is below my design current for my lighting circuit.

C) you choose the method of installation. my lights are in a conduit so I will be using reference method B

I have not gone further than this but once I do I will update on here to help as much as I can.
you have to fill out the table which should of been provided to you. do you have this table??
 
Loki

Loki

-
Esteemed
Arms
Reaction score
473
This question may be answered using the Table 1 or Table 2. It is strongly recommended that you use

pencil when completing the table to allow for recalculation of figures.



Determine, for every final circuit in the café/pool block, each of the following.

a) Design current (Ib)

b) Nominal rating and type of protective device (In)

c) Method of installation reference

d) Rating factors that apply

e) Minimum cross-sectional area of live conductors for current capacity and voltage drop

f) Actual voltage drop.

g) Maximum permissible disconnection time for each circuit as given in BS 7671.

h) Earth fault loop impedance

i) Maximum earth fault loop impedance as stated in BS 7671.

Hi have you done this question? I'm currently working on but having trouble with it

This will help you

20200608_002108.jpg
Use a scale ruler to work out your cable lengths, from memory i think it needed to be no longer than 30m max.
 
OP
H

haroonmahmood

Trainee
Reaction score
4
for question 7 in the assignment their is a question on drawing a explain with an aid of a diagram how electric shock protection is provided by one of the shaver points by electrical separation. I cannot find the correct diagram as the teacher has rejected a couple of my diagrams. could anyone help with this. thanks.
 
Loki

Loki

-
Esteemed
Arms
Reaction score
473
for question 7 in the assignment their is a question on drawing a explain with an aid of a diagram how electric shock protection is provided by one of the shaver points by electrical separation. I cannot find the correct diagram as the teacher has rejected a couple of my diagrams. could anyone help with this. thanks.


A quick google search for shaver electrical separation shows various images showing this.

Post a copy of your drawing so we can see & advise you.
 
Zerax

Zerax

-
Esteemed
Arms
Reaction score
1,441
for question 7 in the assignment their is a question on drawing a explain with an aid of a diagram how electric shock protection is provided by one of the shaver points by electrical separation. I cannot find the correct diagram as the teacher has rejected a couple of my diagrams. could anyone help with this. thanks.
I've just grabbed a copy of "Electrical Installations Book 1" off the shelf (I assume you have a copy ?)... discovered the index at the back of book. There is an entry for Transformer- Isolation, which directs me to Pages 126-7. Nice little diagram and an explanation is all there. Took me all of 30 seconds... and most of that was finding my glasses !
 
DPG

DPG

-
Esteemed
Arms
Patron
Reaction score
11,373
I think your diagram is not wrong as such, but doesn't show the appliance fault part of it.
 
Mark Wright
Reaction score
85
It does seem a bit ridiculous that the tutor doesn't even understand, even if you did a really descriptive drawing and write up because it doesn't have the correct stick man it's wrong?
 
Ljs1996!
Reaction score
0
Hi I need help with question 3 to select a suitable range of protective devices for the contract could someone please explain how I go about doing this thank you
 
L
Reaction score
0
Im a trainee doing c&g2365 level 3 in need of some assistance. how are you supposed to draw the lighting and power arrangements of the pool/cafe areas. tutor just said lines but thats no help. im not after any calculations but maybe a picture of one that has been done for guidance only. ive placed all my lights and power sockets.
 
Loki

Loki

-
Esteemed
Arms
Reaction score
473
Im a trainee doing c&g2365 level 3 in need of some assistance. how are you supposed to draw the lighting and power arrangements of the pool/cafe areas. tutor just said lines but thats no help. im not after any calculations but maybe a picture of one that has been done for guidance only. ive placed all my lights and power sockets.
Hi, As your tutor has said. Draw lines these would be your cable routes. Using a scale ruler & the correct ratio you can measure the cable lengths & use that in your calcs.
 
richy3333

richy3333

-
Mentor
Esteemed
Arms
Reaction score
2,371
Im a trainee doing c&g2365 level 3 in need of some assistance. how are you supposed to draw the lighting and power arrangements of the pool/cafe areas. tutor just said lines but thats no help. im not after any calculations but maybe a picture of one that has been done for guidance only. ive placed all my lights and power sockets.
Our apprentices use excel and the college has predefined shapes to use. Do you not have anything similar?
 