Given the likely Ra of the TT earthing (existing or new), don't you need to put an RCD (100mA, type S?) at the supply end of the distribution circuit to provide protection in the event of an earth fault?

I'd be inclined to put a new rod in for the outbuilding, but connect the SWA armour at both ends, so that you end up with multiple rods for the whole installation. I don't see a need to separate the earthing of the two parts of the system.
 
  • Like
Reactions: 3 people
I would say for separation 1.5 X depth of rod would be sufficient for this installation
 
Given the likely Ra of the TT earthing (existing or new), don't you need to put an RCD (100mA, type S?) at the supply end of the distribution circuit to provide protection in the event of an earth fault?

I'd be inclined to put a new rod in for the outbuilding, but connect the SWA armour at both ends, so that you end up with multiple rods for the whole installation. I don't see a need to separate the earthing of the two parts of the system.

Wasn't the issue to do with it only being a 2c armoured which might not have sufficient csa to satisfy bonding requirements? And if the whole install is on RCBO I can't see what benefit is achieved by adding a 100mA at the upfront end when all it's protecting is one set of internal tails installed in a non-vulnerable method and an armoured cable.
 
Wasn't the issue to do with it only being a 2c armoured which might not have sufficient csa to satisfy bonding requirements? And if the whole install is on RCBO I can't see what benefit is achieved by adding a 100mA at the upfront end when all it's protecting is one set of internal tails installed in a non-vulnerable method and an armoured cable.

OK, maybe it's an unlikely fault, but if the SWA is damaged and the line becomes connected to the armour, what provides disconnection in the time required (1 second for a TT distribution circuit) if it's not covered by an RCD? The cartridge fuse in the KMF won't blow in the required time due to the low earth fault current on a typical TT installation. See 411.3.2.1 and 411.3.2.4
 
OK, maybe it's an unlikely fault, but if the SWA is damaged and the line becomes connected to the armour, what provides disconnection in the time required (1 second for a TT distribution circuit) if it's not covered by an RCD? The cartridge fuse in the KMF won't blow in the required time due to the low earth fault current on a typical TT installation. See 411.3.2.1 and 411.3.2.4

A valid point and one that I actually included then deleted out again on an earlier post as I didn't want to muddy the waters! We usually adhere to the convention that an armoured cable does not require RCD protection - and in this case it seems incredibly unlikely that anyone is ever going to stick a digger bucket through it, either! OK, so add another ££ onto the job and fit an upstream 100mA S type, just for peace of mind. Now, how often do you think that RCD will get routinely tested?
 
  • Like
Reactions: 1 person
Now, how often do you think that RCD will get routinely tested?

About as often as all the other RCDs / RCBOs in the installation, i.e. never, or once every 10 years if the householder is especially diligent and gets an EICR done!
 
when we converted our barn we asked for a separate supply with its own meter to be installed
and letting it selling it etc. does not cause any issues
 
  • Like
Reactions: 1 person
We usually adhere to the convention that an armoured cable does not require RCD protection ...

Yes, if the Zs is low enough to give proper earth fault disconnection by the MCB or fuse, but on TT I'd RCD it every time. I don't see how you can comply otherwise.
 
when we converted our barn we asked for a separate supply with its own meter to be installed
and letting it selling it etc. does not cause any issues

Indeed. Given the sorts of loads that the OP has described, this might well be the best solution, unless the load from the main house is very low.
 
Going back to the question of which end of the SWA should be earthed.
Regulation 542.1.3.3 requires it to be earthed at the installation containing the protective device. In this case the house end of the cable.
Obviously the other option is to connect at both ends.
 
Hmm. Not considered that. Clients are quite specific about what they do an don't like so the location of the new rod was decided by them. If there'd been any choice in the matter I'd have run some new armour clipped to the underside of a raised step across the path straight into the meter box - but that apparently wasn't acceptable aesthetically.....

Anyhoo.
How far apart would they need to be?


Amazing you're actually listening to the clients, that know absolutely nothing about TT systems, and even less than you seem to know, and allowing them to dictate where the earth electrodes are going to be positioned!!!! Who is the paid professional them or You? .... I'm Gobsmacked!!

Get them as far apart as possible, at least 1.5 to 2 X the buried depth. So what are you going to or thinking about bashing in then, ....3/8'' twiggs (eg 1.2m), or a couple 5/8'' coupled together (eg 2.4m depth)??


Not going to go any further, just going to watch and see what happens on this thread...
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Advice for providing power to a barn conversion
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
The General,
Last reply from
Engineer54,
Replies
31
Views
6,379

Advert