At a consumer unit there are a number of seperate radial circuits.

When I remove the line conuctors from the circuit breakers and measure resistance across say any 2 of the radial line conductors I get readings of 500 to 700 ohms using a megger mft 1553 with the dial set to Ω.

When I set the Megger to continuity I get no continuous tone just a succession of fast clicks.

1. Why would there be a resistance at all if they are supposed to be seperate circuits, whats going on?

2. Why is the megger clicking like this?

Thank you.:confused:
 
are the neutrals still connected
if so this is why down 1 live back up n down other n back on 2nd live through the load
the reason it clicks is because the resistance is too high for the ohm meter to beep this only happens on low resistance
 
Well I dont get the symbol that tells me the batteries are weak, though I do get a reading when first switched on that says 9.8v. Any ideas?

Cheers markspark666 of course!
 
Last edited by a moderator:
you can change the continuity ohm setting on the meggers i had a 1502 and had the same problem. it was set to low look at the instruction it is easy to change the setting. i will check tommrrow f you haven't got your manual, But I think you set your meter to ohm's then hold the test button and you can change the setting
 

Reply to Any help appreciated. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
563
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
705
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
Chaps - having problems with a new Megger MIT420/2 insulation/continuity tester 'oscillating' and failing to give stable resistance readings in...
Replies
2
Views
620

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock