i think that flex shield is still to be recognised by bs7671 as a cable type that doesnt need rcd protection , like pyro & swa , thus has limited use.
its biggest obstacle is its limited to 170A fault current , as stated in the advert.
 
i think that flex shield is still to be recognised by bs7671 as a cable type that doesnt need rcd protection , like pyro & swa , thus has limited use.
its biggest obstacle is its limited to 170A fault current , as stated in the advert.

If its BS8436 then it is recognised by BS7671 - see 522.6.5 (that was the BRB - green book is in the van!)

Obviously as its limited to 170A can only be used on circuits up to B rated 32A MCBs.

I did a whole house in this because I couldn't run cables through floor joists. Old (1700s) house!
 
If its BS8436 then it is recognised by BS7671 - see 522.6.5 (that was the BRB - green book is in the van!)

Obviously as its limited to 170A can only be used on circuits up to B rated 32A MCBs.

unfortunately alot of rcbos these days are in the type C flavour , even for domestic Cu's depending on the brand.
an unwarey installer may get caught out by its limitations so its use should be cautious if not using rcd protection , just a thought.
 
unfortunately alot of rcbos these days are in the type C flavour , even for domestic Cu's depending on the brand.
an unwarey installer may get caught out by its limitations so its use should be cautious if not using rcd protection , just a thought.

But this negates the need for RCBOs, relying on the over current functionality of MCBs to disconnect a fault, type B MCBs are widely available.
 

Reply to Any one flexishield cable befour in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
842
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
875
Is blue neutral or earth when there is a black cable (which is the old neutral) - old system? Other one is red, no green / yellow
Replies
6
Views
312
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
596
Seen a couple of videos with Doncaster cables now producuing a T&E with the CPC already sleeved so no need to fit our own. I also read somewhere...
Replies
19
Views
688

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock