How come MICC glands don't with a banjo where as SWA does, yet both are required to the connected to earth or are used as a CPC?
 
Sorry are you talking about the pots with the soldered earth connection inside?

On the termination iv done, its only been 2 core into a metal back box.
 
If the pyro gland back nut isn't tightened up onto the olive then a banjo/frying pan isn't going to do much. Earth tail pots aren't really needed unless glanding into plastic, geez bare pyro now that takes me back.
 
Pot earth tails weren't around, and banjo's weren't really required when i first came into the industry, ....but i can't think of a single instance where we didn't achieve dam good earth connections. If your that bothered about a MICC not giving you a good earth connection, use Piranha nuts, far better than a banjo...
 
Installed loads of pyros prior to earth pot tails arriving on the scene, never any problems. Only time ever fitted banjo's.....with swa.
 
It all comes down to the item/equipment you are terminating into. If its a besa/metal conduit box and you are using the threaded spout then no banjo is required for either micc or swa cable.
 
Our fire alarm installation over the whole project is wired in MICC, i'm pretty sure that we are not using pots with incorporated earth tails on our installation. I know we didn't on the last project. And i won't be giving it a second thought either!! lol!!
 

Reply to Banjo in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
I’ve had a weird one today. Banjo having 50v on it. L - main earth = 230v L - N = 230v N - main earth = clear I have 50v on the live - banjo &...
Replies
4
Views
678
As a trainee can I ask why the banjo is on the outside of the Wiska box. I understand that the earthing of the SWA must be maintained but would...
Replies
9
Views
1K
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
2K
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock