Any help or advice would be great...

Builder called me today, saying he's refitting a bathroom. And needs me to do electrical work. Done this type of work for him many times .

But this one isnt so straight forward. Needs new IP lighting, Ex fan, and supply for shower.
Takes a look at the board and finds its an old wylex fuse board thats been converted to accept breakers.
Normaly would fit 2 way board with 63amp RCD Incomer. Or RCBO's if the existing board could accept them. Worse case would be replacement consumer unit.

Now my problem is where the incoming supply/meter is located.. about 6 meters away outside In a wall mounted cabinet. The existing tails run through conduit between the brick cavity of the house, making it even worse by the fact it also goes around the corner of the building. Now this would prove a total pain to replace the tails or install another set for a two way board. Now am not aware of any RCBO's that fit this type of wylex board..

Any tips or solutions would be great. Come across this type of board before bit supply/meter was only ever a few feet away.
 
Why not divert the existing tails into a henly block by the DB, saves any wiring. Would also suggest fitting a switch fuse on the tails at the meter too.
 
  • Like
Reactions: 1 person
haha funny looking choclate blocks might just keep to henlys from now on just in case any one gets the wrong idea ha
 
Last edited by a moderator:
Thanks for the replies..
Again i would normally use a henley block as suggested. But this board is a recessed type in the hallway wall.
If it was under the stairs or in a cupboard i would do just that. There isnt anywhere practical for me to mount a henley block.. Any other suggestions or info on where a henley block can be mounted with regards to the regs..
 
Last edited by a moderator:
can you not replace the board with a new 17th edition recessed board from wylex?
 
yeah i can do that. but again i come across that monster problem of renewing the tails back to meter position.
Which if at all possible i wanted to avoid.
 
16mm tails at the moment.
The local council always wants 25mm with a DB Change.
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Bathroom electrics ( Recessed wylex board )
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
mikeymoo,
Last reply from
mikeymoo,
Replies
19
Views
3,644

Advert