M

m1ck_b87

I'm testing street lighting which has 10 sodium lights over a space of about 200m wired in 3 core 4mm armoured underground, this is protected by a 16 amp mcb. I've done a Zs and its greater than the max Zs values for the 60898 type b, what is the easiest way of working out the load.
 
what rating are each of your lamps in the fitting?

Find out how many lamps you have on the circuit in total and find the total rating of the circuit in Watts (Power)

Power / Voltage = Current.

so say each lamp was 200Watt

2000/230V - 8.69Amps.
 
UM, well that could be a problem, I would bet 10 sodium street lights over 200 mtrs of cable would trip haha, m1ck, whats the ZS reading?
 
Zs reading was 3.64 and it has a contactor I was thinking of down grading to a 10 amp that's why I wanted to work out a accurate load
 
I'm testing street lighting which has 10 sodium lights over a space of about 200m wired in 3 core 4mm armoured underground, this is protected by a 16 amp mcb. I've done a Zs and its greater than the max Zs values for the 60898 type b, what is the easiest way of working out the load.

Hi M1ck,

I don't want to seem rude but you are testing street lighting yet asking on a forum how to calculate design current?
 
whichever way you work it out don,t forget the power used will be a little more than the 70W stated for the lamp,due to losses in the control gear etc,on a single lamp this may not matter but on a run of them well it may be something you need to allow for.
 
A Test with clamp on amp meter with all the lights running will soon give you the full load,but if the lamps are 70watt the load will be well under 10amps in which case you zs of 3.64 will be fine with a 10amp type B or you could go to a 6amp type C
 
Test with clamp meter and assess load in reference to the design current for the circuit.
Measure R1+R2.
Measure Zs at distribution board.
Measure Zs at circuit.
Look for any abnormal results across the above ^.
60898 Type B 6Amp or 10Amp will be fine IMO.
 

Reply to big problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
904
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
841
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
777
when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...
Replies
2
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top