Discuss Breaking capacity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
Hi can anyone advise me. My company have installed a dimming rack ( from USA ) it's a 0-10 v dmx system . It's 3- phase and protected by 3- phase B 20 amp 60898 but on the dimmer rack it has 24 x C10 amp 60898 but they only have a breaking capacity of 3 KA my Pfc reading is 2.9 so it exceeds the B/C as the main 60898 has B/C of 10 K/A is this covered I know under fault condition the dimmers can melt but it will trip through main mcb . Where does that leave me with certification ? Can anyone help please
 
It's not a fixed part of the installation, it's an appliance. However, I would look at uprating that B20.....what's the dimmer rack driving?
 
Hi thanks for your reply it's a 3- phase 20 A but it's only doing led lights. So regarding certification the 3- phase mcb will meet requirements even though each led circuit goes straight back to the dimmer rack and there individual mcb only have a B/C of 3K/A and my Pfc is 2.9 and if I'm right in thinking you have to double this reading as it's 3- phase so would exceed the rating on the dimmer panels mcb s
 
where are you measuring that 2.9kA? before the 3kA breakers or after?
 
Its single ph circuits, each to an MCB which the manufacturer has built and specified as they wish - its not your responsibility. You only have to answer for the upstream breaker, and as I said earlier, you may have some issues with 8 x C10's feeding from a B20 due to inrush current, so look to upgrade that breaker to at least a C32/3. The internals of the dimmer handle everything else and ffs don't megger it!!
 
Out of interest, which brand of dimmer is it?
 
It's a unison DRd6 electronic theatre controls Middleton wi USA

LOL - AKA an ETC theatre rack. What's the application? Odd choice of weapon for a standard architectural install.
 
those MCBs only need to be rated for the kA value after the MCBs.

Tel - doesn't quite work that way. The individual channel MCB's exist solely to protect the channel Triac inside the dimmer / functional isolation, and the pfc of the individual circuit will not resemble the pfc of the incoming arrangement. In fact, you can't (really) in any meaningful way test for the pfc of the outgoing circuits as they've become chopped electronic waveforms via a bunch of timers and triacs. So long as the upstream CPD is rated properly for the right level of 3ph PFC then all is well. What happens after it enters the box is all smoke and mirrors!
 
i stand corrected. no knowledge of these dimmer arrangements, so will bow to your suprior knowledge on this.
 
Tel - doesn't quite work that way. The individual channel MCB's exist solely to protect the channel Triac inside the dimmer / functional isolation, and the pfc of the individual circuit will not resemble the pfc of the incoming arrangement. In fact, you can't (really) in any meaningful way test for the pfc of the outgoing circuits as they've become chopped electronic waveforms via a bunch of timers and triacs. So long as the upstream CPD is rated properly for the right level of 3ph PFC then all is well. What happens after it enters the box is all smoke and mirrors!

Whilst my learned friend is quite right about the Pfc after the dimmer, I'd point out that the outgoing wiring from it still needs to be tested properly, just in case his comments are misunderstood.

Personally I treat each dimmer as if it was a DB and each one gets a test results sheet. You can easily do all of the tests without causing any trouble to the electronics, just have to use the alternative method of Zs testing where you link L and E at the far end of the circuit.
 

Reply to Breaking capacity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
628
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
597
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
Replies
0
Views
732

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock