My parents are building a house in Ireland, but the architects drawings make no mention of BS7671 under the electrical spec. I was thinking of going over there to do at least 1st fix for them.

Does anyone know if the 17th holds weight in Ireland, or in fact any other countries at all?? Or will there always be different regulatory exams to pass for each different country?? I have 17th, C+G 2 and 3.

Cheers,
Myles

Its southern Ireland btw :)
 
Last edited:
Oooops decided to open my eyes and wake up BS 7671 covers England Wales Scotland and Northern Ireland but not Southern Ireland.

Back off to sleep now

Chris
 
You will have problems getting your house connected.
If you do not have the right to self-certify (Be a member of RECI or ECSSA) then you will have to get an inspector in to test the house for you, apart from the fee (approx €350) you will need to show him you carry Irish accepted public liability insurance.
Its also important to note that Irish earthing standards are miles ahead of UK standards and require equipotential cages in all bathroomsand RCBO's for individual showersand bathroom lighting circuits. There has been a move away from ring socket circuits lately and now radial socket circuits are preferred. You will need 2 seperate circuits for the kitchen, and 1 circuit for two rooms throughout the rest of the house. All houses in Ireland are TNCS and so require an earthing rod.
 
Thanks for all the replies.

Bazza, if Ireland is mostly Tncs surely I would be earthed to neutral not earthing rod?? Do you mean TT??

Cheers,
Myles
 
No, TNCS.
Neutral and Earth are combined at the pole IIRC. I usually run a 16sq earth to the rod and 10sq to the hotpress. 2,5sq earth from the board to each bathroom and one from the board to the kitchen sink. It used to be acceptable to run the kitchen sink earth back to the nearest socket, but sine they done away with ring circuits, it has to go back to the board now.
 
No, TNCS.
Neutral and Earth are combined at the pole IIRC. I usually run a 16sq earth to the rod and 10sq to the hotpress. 2,5sq earth from the board to each bathroom and one from the board to the kitchen sink. It used to be acceptable to run the kitchen sink earth back to the nearest socket, but sine they done away with ring circuits, it has to go back to the board now.
The ESB (southern ireland REC) uses a neutralizing earth system which is identical to the PME protective muliple earthing system TN-CS which is used in the UK recs. the link between Neutral and earth is done at the cut-out position and not the pole. ESB also provide an isolator at meter position for customer tails to be installed by electrician. A spike must also be provided by spark and as far as i know 10sq earth is acceptable but 16sq obviously better.:)
 
Last edited by a moderator:

Reply to bs7671 in Ireland?? in the Ireland area at ElectriciansForums.net

Similar Threads

T
apologies if this has been covered before im finding my feet around here:ninja: ive recently qualified as an elctrician in ireland i was fortunate...
Replies
2
Views
1K
T
G
I qualified in the 'city and guilds' method, and learnt the hard way pulling cables and chasing walls, now I have my own company and I am having a...
Replies
13
Views
1K
Giovanni
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock