I'm in the process of changing my MR16 bulbs to LEDs. I've manged to cut out most of the transformers and wire in a at GU10 lamp fitting which has worked fine.

However I have run into a little problem. I have pulled down a couple of transformers which appear to have to have 2 main cables running into them (2 Neutral & 2 Live) . It appears one of the cables is looped to the rest of the spotlights in the room. Previously i have only encountered 1 cable running into the transformer, which i have then cut out and wired in the GU10 lamp.

I guess my question is how can i connect the loop and the bulb together as they all previously ran through the transformer?

I have included pictures.

Many thanks,

Harry
 

Attachments

  • IMG_7115.jpg
    IMG_7115.jpg
    83.5 KB · Views: 29
  • IMG_7119.jpg
    IMG_7119.jpg
    69.3 KB · Views: 29
it's just a loop in and out. most LED fittings allow for 2 x L and 2 x N. if not, use wagos in a wago box at each point. 2 cables in and 1 out. remember to make the cpc (earth) continuous even if the new fitting don't need earthing. just looked at the 2nd pic. seems someone has cut off the cpc's. these need the cables stripping back and reinstating, with green/yellow sleeving added.
 
Last edited by a moderator:
it's just a loop in and out. most LED fittings allow for 2 x L and 2 x N. if not, use wagos in a wago box at each point. 2 cables in and 1 out. remember to make the cpc (earth) continuous even if the new fitting don't need earthing. just looked at the 2nd pic. seems some idiot has cut off the cpc's. these need the cables stripping back and reinstating, with green/yellow sleeving added.

Thank you i didn't realise i could just connect directly into the LED fitting. You're right it doesn't look like the fittings need earthing, but i'll strip the wires back and add some
green/yellow sleeving.

Thanks again
 
post a photo of the terminals in one of the LED fittings.
 
I might be misunderstanding but some of the old ones had a big transformer then they all just plugged in like a daisy chain to each other if that's what you've got you'll need to pretty much replace the lot
 
I might be misunderstanding but some of the old ones had a big transformer then they all just plugged in like a daisy chain to each other if that's what you've got you'll need to pretty much replace the lot
he's ripping the transformers ot and daisy chaining 240V GU10 fittings.
 
  • Like
Reactions: robd
Hi

I'm in the process of changing my MR16 bulbs to LEDs. I've manged to cut out most of the transformers and wire in a at GU10 lamp fitting which has worked fine.

However I have run into a little problem. I have pulled down a couple of transformers which appear to have to have 2 main cables running into them (2 Neutral & 2 Live) . It appears one of the cables is looped to the rest of the spotlights in the room. Previously i have only encountered 1 cable running into the transformer, which i have then cut out and wired in the GU10 lamp.

I guess my question is how can i connect the loop and the bulb together as they all previously ran through the transformer?

I have included pictures.

Many thanks,

Harry
post a photo of the terminals in one of the LED fittings.


Hi, this is the fitting
 

Attachments

  • fitting.JPG
    fitting.JPG
    80.5 KB · Views: 24
Hi, this is the fitting
if that cable clamp is big enough for 2 cables, then loop at the terminal block. also they come with an earth connection. cpc's should be terminated so as to earth the metalwork of the fitting.
 
if that cable clamp is big enough for 2 cables, then loop at the terminal block. also they come with an earth connection. cpc's should be terminated so as to earth the metalwork of the fitting.

Thanks mate. Once i've stripped back the cable to reveal the earth, do i cover the earth with green/yellow sleeving and tape? or connect them to earth clamp at the terminal block?

IGNORE Above.

Thanks for your help mate. Really helpful!!
 
Last edited by a moderator:
and use 2mm earth sleeve.
 
I’d put the house fixed wiring in a joint box (as previously suggested) then flex to each down light. Either a Wago, or my fav for down lights a Click CT102C;
 
  • Like
Reactions: telectrix
Does that connection have an enclosure which goes around it. I see it encloses the live and neutral but not the earths. To me that leaves them not suitably enclosed.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Changing MR16 to LED
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
12

Thread Tags

Advert

Thread statistics

Created
HarryB1987,
Last reply from
westward10,
Replies
12
Views
2,211

Advert