dim_bulb
regarding post 18 - wont need to take an earth to the switches if they are plastic or are they metal switches?
Discuss Class I light fittings, no Earth, what would you do? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Oops, misread. I was thinking about something else. Thanks Spark
I've come across downlght fittings that were originally MR16 SELV and don't have a cpc connection point. Then they've been converted to a GU type lamp at a later time which renders them non compliant with the regs.
Post 22 reg.412.1.3 if its not used as sole protective measure ie use of rcd would it satisfy reg 412.2.3.2?
Reply to Class I light fittings, no Earth, what would you do? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net