On this occasion, 32A + 16A =48A
The other options are probably not available.
What did the electrician that came out say?
After all they have the best information and knowledge of the installation.
On every occasion 32 + 16 =48,thats a simple mathematical truth.
However that is not the correct way to calculate th eload on this circuit, you need to apply diversity.
applying diversity to 48A. ( 10A+ (38A x 0.3)) = 21.4A. add 5A if isolator has a built in socket.
Reply to Cooker installation advice in the UK Electrical Forum area at ElectriciansForums.net
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Is this ok? 32amp breaker with a 6mm wire leading to fused cooker switch. This then leads with 6mm cable to hardwire point. Can i hardwire 2 x...
OLDBOY
O
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...