mak
On a ring main we test r1r2 at every outlet since there is no end of the circuit and every test should return same-ish figure unless there is a loose connection or socket is on a spur, right?
What about the the radial circuit? Other than to check polarity is there a point to test anywhere other than at the switch i.e. end of the line? Unless the reading at the end of the line is higher than expected?
Zs which is earth fault loop (R1+R2+Ze), we test the impedance to make sure in case of a fault on a circuit the protective device will react before the wire will melt into soup?
I remember there was a formula that explained this, something like design current ≥ conductor current ≥ fault current.
An appliance with a double pole switch fed from an outlet with crossed line and neutral will not get damaged unless it is polarity sensitive, if there is one?
Thanks.
Thanks.