M
mwigham85
I recently asked what the max zs would be for a Crabtree C50 7.5a breaker and didn't find the answer but if any one else ever needs to know here's a formula take the breaker rating 5,7.5,10 etc multiply by ( 4 for type1) (7 for type 2) and (10 for type 3) then divide 230v by that value once you have your max permitted zs multiply it by 80% so for a Crabtree C50 type 2 7.5a you would do 230v divided by (7.5x7) x 0.8 which equals 3.50 zs
This is the old way of doing it , now we also use cmin so If you multiply your answer by 0.95 it gives about 3.33 ohms
Reactions: Briggs12345
Crabtree C50 max zs
Periodic Inspection Reporting & Certification
Thread Tags
mwigham85,
newfutile,