Hi all.
Did an EICR today on a rented property that had a CU change about 8 years ago.
Found a few things wrong, the main issue really is that a few sockets are fed in 1.5 from the ring and a couple of wall lights are fed of the ring as well in 1.5.
Just wondering how much testing you guys do after or before a CU change? IR and closed rings and visually looking at bonding, cpc's present, rubber etc as not everyone will pay for a pre-change EICR.
If you're doing an install and do the end to end from the CU and the cross connection, and the readings are going to pass, would you drop any of the socket plates for a visual inspection?
 
Hi all.
Did an EICR today on a rented property that had a CU change about 8 years ago.
Found a few things wrong, the main issue really is that a few sockets are fed in 1.5 from the ring and a couple of wall lights are fed of the ring as well in 1.5.
Just wondering how much testing you guys do after or before a CU change? IR and closed rings and visually looking at bonding, cpc's present, rubber etc as not everyone will pay for a pre-change EICR.
If you're doing an install and do the end to end from the CU and the cross connection, and the readings are going to pass, would you drop any of the socket plates for a visual inspection?
Always do an EICR before a CU change to help avoid my backside getting bitten after the change.
 
Hi all.
Did an EICR today on a rented property that had a CU change about 8 years ago.
Found a few things wrong, the main issue really is that a few sockets are fed in 1.5 from the ring and a couple of wall lights are fed of the ring as well in 1.5.
Just wondering how much testing you guys do after or before a CU change? IR and closed rings and visually looking at bonding, cpc's present, rubber etc as not everyone will pay for a pre-change EICR.
If you're doing an install and do the end to end from the CU and the cross connection, and the readings are going to pass, would you drop any of the socket plates for a visual inspection?
If changing CU then I try to do an effective EICR beforehand, though don't always tell the client that's what's happening.

If R1+R2 is fine at every socket, I won't always drop socket plates, especially if they are painted in, etc. I'd be much more likely to if the property was older than 60s and there was a chance of rubber cabling around.

I will usually check lights more carefully, especially any that look suspiciously DIY added...

There is a whole best practice guide on changing a Consumer Unit which details the minimum that should be done and doesn't mention dropping sockets.

Of course a single spur socket could in theory be run in 1.5mm if all necessary requirements are met (no derating, etc - which might be unlikely to be fair), I believe it used to be specifically mentioned as a possible allowed method in an older version of the OSG?
 
I just checked Appendix 15.
1.5mm spurs are only permitted via a FCU.
I have a feeling it might have changed in recent editions, or more specifically that in a previous version of book or OSG it was less clear that it had to be a Fused Spur.

Possibly in the 16th, which is what I first trained in, though can't see anything from a quick skim - just a vague memory.

Though really no good reason for not using 2.5 in any case these days - just that there might have been a time when it was arguably "compliant" - surface clipped short run with no derating to single socket, for example...
 

Reply to CU Change Testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
815
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
836

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock