Hi with a 100A 1361 cut out and 100A main switch in the CU , when fitting a switched fuse unit in a long meter tail run would you make it 80A to allow for descrimination of the fuses. Cheers
 
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
E

ezzzekiel

  • Thread Starter Thread Starter
  • #2
1361 will handle lot more than stated 100a
 
B

blenki

  • Thread Starter Thread Starter
  • #3
Are you saying you would put a 100A in , i thought you had to apply discrimination to ensure that if theres a fault on the meter tails the switched fuse unit would blow and not the 1361
 
S

Spudnik

  • Thread Starter Thread Starter
  • #4
Ideally what you stated is correct, to allow for discrimination.
 