SpannerSpark

Hello all,

I have just installed new circuit for a friend from an existing install. The new circuit is fed via underground SWA (from an old building) to a new building. In the new building I have fitted a 2way CU with combined main switch/30mA RCD (new type RCD BS61009) and two MCBs (lights & sockets). The only CU in the old building (the feed to my new circuit) is an old wylex metal clad with a old style single main switch/30mA RCD (WSES80/2F BS4293?) covering all circuits. Therefore i told my friend that I would need to add a new small CU in the old building or in some other way provide some discrimination between the old and new 30mA RCDs. He said he would really like the install to work sooner rather than later and so i agreed to test my new install and then temporarily fit the new circuit to the old CU. I explained that any RCD trip type fault would most probably take out both RCDs and all circuits. The new circuit tested out exactly as expected, all good. The system worked for a couple of days and then the old RCD tripped, was reset and then a couple of days later tripped again. Is was then than i was in a position to install the new CU in the old building, protected my new circuit on the new CU (main switch and 32A MCB only as the earthing system is TNCS and the distribution circuit Zs was low enough to not need a 100mA type. Since then all circuits have behaved 100% ok (another two days). I have checked and rechecked my measurements, all spot on (e.g insulation res >500M all circuits inc distribution SWA). i was wondering if the old style RCDs worked differently and could in some way have a problem being connected to a circuit with a new style RCD in it. :confused:
I know that now my distribution circuit has no RCD then any latent fault before the new CU RCD wont show up, thats why i have remeasured my circuit and its spot on.
 
Its a wylex "NSB" series (i think thats right), the one with the dedicated extra busbar connection on the MSBs, looks like a good design to me everything is connected via screw terminals, nothing loose, I dont think its a connection problem.
I have just thought of something i didnt put in the original post (and i should have done), the install had 2 PV panels added to it a few weeks before i did any work on the CU (not by me) feeding into the old CU, they were only fired up @ a week before i started my work. So i guess the tripping could also be something to do with those. Could the PV feeding into the CU cause the trip? I suppose that brings me back to how do new and old types of RCDs work. i know really old ones are voltage operated (VOELCB) but i dont know if the wylex one i described in the original post is one of these or is similar to the newer RCDs design in that it genuinely detects difference in current flow between L-N lines.
 
Did you try a ramp test on the old RCD. If it was an old BS 4293 then it could very well be 15 yrs old as these were replaced back in the mid 90's

You may just find that the old RCD was triping at a lot lower mA range. You may well find that the PV invertor could have been producing enough High Protective Conductor currents to trip that old RCD
 

Reply to Do old type RCDs work differently to new type? in the Australia area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
732
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
439
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
899
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
634

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock