If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Hello.
I'm in the final stages of completing my electrician course, and I find myself confused (again) by EFLI.

In the textbook provided is this:

Uo 230V
see below for each circuit.

Calculate the maximum Zs for each circuit:
Complete the table.

The answers given in the textbook are said to be correct.

However, according to BS7671, the values in the textbook exceed the maximum allowed Zs.

Eg: For the outbuilding circuit, BS7671 states type B 20A has max Zs of 2.19 ohms, yet the book says the correct answer is 2.30 ohms?

Am I missing something here?
Please can anyone help with this?
Thanks,
Gary

IMG_6256.jpg

IMG_6250.jpg

IMG_6237.jpg

IMG_6235.jpg
 
Last edited:
Ok, issue sorted.
According to the tutors, the answers in textbook are prior to amendment 3 and even though the version textbook was printed”after” amendment 3, somehow it didn’t get updated too.

So after applying Cmin factor 0.95, it brought the answers down to where they should be!
 
  • Like
Reactions: Strima
even before amd 3 and Cmin. ( which is to allow for supply volts down to 218V ), correction factor for cable temperature was to allow for temp. to be 70 deg.C, i.e . a factor of 0.8. applied to the BS7671 tabulated figures.
 
They have left out the correction factor Cmin.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Peterborough
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Earth fault loop impedance - textbook values vs BS7671
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Gary Tollison,
Last reply from
Risteard,
Replies
4
Views
4,826

Advert