I am about to wire my own integral garage. I use it as a workshop so I am thinking about running singles in galv conduit. I've not used singles before and I've only ever used galv conduit to protect T&E run outside of safe zones.

I haven't been able to find any good information on singles / conduit – either books or internet resources (I would be interested if anyone can point me at any) – so I have some rather basic questions I'm afraid. Really, it's earthing that I am unsure of …

I'm planning on running the T&E from the ring main and lighting circuit from an adjacent room through the wall into a conduit box in the garage and then using wagos to go from T&E to singles. I'm planning on running the ring main and lighting circuit in the same galv conduit, each with it's own cpc … I assume that this is correct?

So far it seems the same as T&E except I've got conduit instead of sheaths (ok, I know that switch drops are normally wired a little differently). The problem comes when I earth the conduit … how should this be done? I assume I should use a flying lead from each socket / switch plate to the metal box, but this will connect the cpc of the lighting circuit and the cpc of the ring main together … is that correct / ok?

How does that effect testing? Should I check cpc continuity before connecting the flying leads to boxes / conduit?

I suppose I could just use PVC conduit instead, but I would rather learn how to do it properly :)
 
Conduit can be used as a cpc, but in your instance I would probably continue the cpc's as it forms part of a T+E circuit. It doesn't matter that the earths of each cct. are joined together, just write down the readings you get, think of the conduit as extra cable. You can do an r2 test on all points of the conduit instaed of doing r1+r2
 
You will also find that the conduit boxes have a 4mm earth lug connection in them. You can use this to earth your conduit.
 
Conduit can be used as a cpc, but in your instance I would probably continue the cpc's as it forms part of a T+E circuit. It doesn't matter that the earths of each cct. are joined together, just write down the readings you get, think of the conduit as extra cable. You can do an r2 test on all points of the conduit instaed of doing r1+r2

Thanks.

What's the advantage of measuring R2 instead of R1+R2 for points on the conduit?

Should R2 be measured with the parallel earth paths in place?
 
You will also find that the conduit boxes have a 4mm earth lug connection in them. You can use this to earth your conduit.

Thanks.

Are you suggesting that the conduit only needs to be earthed at one point, i.e. the lug in the conduit box?

Does it need to be connected to the cpc's of all the circuits that it contains or only to one of the circuits?
 
if you are using cpc's then the conduit itself will be earthed as long a it's all metal. you only need to fly lead the metal box where you are changing from T/E to singles. wire the N direct to the lights, and the L's through the switches.
 
if you are using cpc's then the conduit itself will be earthed as long a it's all metal. you only need to fly lead the metal box where you are changing from T/E to singles. wire the N direct to the lights, and the L's through the switches.

Thanks.

Makes sense. One question though ... should I connect he cpc of both circuits to the conduit box or just one of the circuits, say the ring main?
 
Now I think about it, there are other situations where the cpc's of various circuits get connected together anyway ... like the "illustration of earthing and bonding conductors" in approved doc P which shows cpcs from a towel rail circuit, shower and lighting circuit all connected together via supplemental bonding in a bathroom ... so I guess that I shouldn't worry about that at all and connect the cpc of the lighting circuit and the cpc of ring main to the conduit at the point where it goes from T&E to singles.
 
yes. or you could dispense with cpc cables and use the conduit as cpc. less cable pulling. more air space in the conduit.
 
  • Like
Reactions: 1 person
you can't beat a nice tight bush.
 
  • Like
Reactions: 4 people
just TT the tree.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Tuttle

Arms
~
Joined
Location
Berkshire

Thread Information

Title
Earthing galv conduit containing multiple circuits
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Tuttle,
Last reply from
telectrix,
Replies
15
Views
4,947

Advert