Bob Geldoff1234

-
Esteemed
Arms
Reaction score
767
On a domestic property,owned by the householder, the general opinion on no rcd protection is a C3 as long as other conditions are met.So therefore the EICR could get a satisfactory on it.

Move onto rented properties and it's my take that the rules change.
Suddenly no RCD protection becomes a C2 due to the rented sector requirements and the EICR would get an unsatisfactory.
Is this correct?
Does this also mean that storage heater circuits on their own consumer unit would have to be upgraded to have RCD protection if in a rented property?

Quite frankly it's all very confusing
 
I agree with above, no change to codings, whatever you would normally give still stands - you're still inspecting the installation based on the requirements of and compliance with BS7671 and essentially whether or not it is dangerous.

Just out of interest, why would you think the coding would change? I'm asking as I've seen and heard a lot people saying similar things since the eicr's became a rental requirement. Someone tried to tell me only the other day that all plastic consumer units in rental properties must be replaced with metal by the end of next year!
 
On a domestic property,owned by the householder, the general opinion on no rcd protection is a C3 as long as other conditions are met.So therefore the EICR could get a satisfactory on it.

Move onto rented properties and it's my take that the rules change.
Suddenly no RCD protection becomes a C2 due to the rented sector requirements and the EICR would get an unsatisfactory.
Is this correct?
Does this also mean that storage heater circuits on their own consumer unit would have to be upgraded to have RCD protection if in a rented property?

Quite frankly it's all very confusing
Where are you getting the information that new rented property differs from an own property . You should treat them all the same they are domestic propertys . Also you cant just blanketly code no RCD protection . You must break it down to..

Rcd protection for socket outlets
Rcd protection for socket outlets that can be used outdoors
Rcd protection for lighting circuits
Rcd protection for cables buried in walls less than 50mm deep
Rcd protection for cables in metal partition walls
Rcd protection for circuit's within a special locations

All the above are coded differently.
I'm sure there is some more but you can use them for starters :)
 

Reply to Eicr codes for rented properties? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
707
I recently had and EICR done and received an 'unsatisfactory' report due to not all circuits being RCD protected on the consumer unit. The...
Replies
16
Views
4K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock