pc1966

Esteemed
Arms
Reaction score
11,984
Many years ago I fitted some RCD socket outlets to my parents home for the two likely to be used outside, the front hall and the kitchen one next to the window. Being the paranoid sort of person I am I always test-trip them when I have cause to use one, and in the case of the front hall that is any time helping out with hoovering. Yesterday it failed to trip so today included a trip to Toolstation for a modern replacement. I wondered how old it was so opened it up out of curiosity and found a couple of 1989 date-codes, so not too bad to have lasted for 32 years energised.
rcd-1.jpg
rcd-2.jpg
rcd-3.jpg
rcd-4.jpg
rcd-5.jpg
In the last one you can see the light-grey VDR included for surge protection (lightning would blow the PCB tracks I guess as "ultimate fuse") just above the bridge rectifier, and the three parallel 120K dropper resistors taking the 340-ish volts crudely smoothed DC from that down to something like 15V for the 741 op-amp. Adjustable trip as well!
 
Many years ago I fitted some RCD socket outlets to my parents home for the two likely to be used outside, the front hall and the kitchen one next to the window. Being the paranoid sort of person I am I always test-trip them when I have cause to use one, and in the case of the front hall that is any time helping out with hoovering. Yesterday it failed to trip so today included a trip to Toolstation for a modern replacement. I wondered how old it was so opened it up out of curiosity and found a couple of 1989 date-codes, so not too bad to have lasted for 32 years energised.
View attachment 104794
View attachment 104795
View attachment 104796
View attachment 104797
View attachment 104798
In the last one you can see the light-grey VDR included for surge protection (lightning would blow the PCB tracks I guess as "ultimate fuse") just above the bridge rectifier, and the three parallel 120K dropper resistors taking the 340-ish volts crudely smoothed DC from that down to something like 15V for the 741 op-amp. Adjustable trip as well!

Good old 741 op amps. I wonder how many of those have been sold over the years!

Any of the capacitors bulging?
 
Did you manage to fit that in a flush mounted box dating back over several decades?
The original socket was single gang, at the time those RCD sockets were all dual-gang so mounted in a surface box. I could have gone back to single gang now, but then I would have to reinstate a back-box and, more seriously, fill the screw hols and repaint around it as 30 years on it ain't going to look good underneath. Below is the replacement:

rcd-new.jpg
 
Good old 741 op amps. I wonder how many of those have been sold over the years!
Must be one of the most successful ICs of all time, not just the '741' but all of the upgrades that followed with JFET or MOSFET inputs, etc.
Any of the capacitors bulging?
No electrolytic used, only "big" capacitor is a tantalum bead (yellow thing next to the trim-pot). The only concession to cost seems to be a single-side PCB with the occasional pink wire link. The use of tantalum cap and metal film or metal oxide resistors is good, so partly explaining its 32 years operating life!
 
Can't see the new one lasting 32 years. Can't even get a floodlight to last over 3 sometimes now
Very true, but my parents won't last that long either :(

Really the house could do with being rewired as it is still mostly imperial cable (since it was rewired a little before they moved in 1972, with the odd bit added/modified in the kitchen in the 80s) along with a new CU so RCD protected at source, but that would be a nightmare for me and my parents (for opposing reasons) and given this at least ticks the box for RCD protection where most needed, it will keep them going for as long as necessary.
 
Very true, but my parents won't last that long either :(

Really the house could do with being rewired as it is still mostly imperial cable (since it was rewired a little before they moved in 1972, with the odd bit added/modified in the kitchen in the 80s) along with a new CU so RCD protected at source, but that would be a nightmare for me and my parents (for opposing reasons) and given this at least ticks the box for RCD protection where most needed, it will keep them going for as long as necessary.

The world is not a perfect world. DPG 2022.
 

Reply to Failed RCD socket given post-mortem out of curiosity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
356
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I have a pressure washer that I got as part of "a good deal", actually an exceedingly good deal as I later found out. I've had it a while, I guess...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock