Hi,

I have just finished off a kitchen and swapped the CU out at the same time...

Part of the run of the cable goes under the kitchen floor in a duct...

Its 2m long the duct.

When applying rating factors, is there a min and max length in comparison to the overall length of the run?

I have 5 lots of twin and earth running in a duct, strictly speaking I should apply a factor of 0.60 to them but if it was only 2m long does it really need it applying?
 
Yes, you do have to de-rate, and also make sure the ducting/trunking is large enough for the cables. If the tables do not show the cables you are using, a 45% 'empty' should suffice - that means the trunking / conduit should not be more than 55% full by volume - or it could be only 45% full, cant remember properly now without going out to get the book out.

It's all in easily readable form in the on-site guide Appendix E.
 
Hi,

I have just finished off a kitchen and swapped the CU out at the same time...

Part of the run of the cable goes under the kitchen floor in a duct...

Its 2m long the duct.

When applying rating factors, is there a min and max length in comparison to the overall length of the run?

I have 5 lots of twin and earth running in a duct, strictly speaking I should apply a factor of 0.60 to them but if it was only 2m long does it really need it applying?

Yes, you do have to de-rate, and also make sure the ducting/trunking is large enough for the cables. If the tables do not show the cables you are using, a 45% 'empty' should suffice - that means the trunking / conduit should not be more than 55% full by volume - or it could be only 45% full, cant remember properly now without going out to get the book out.

It's all in easily readable form in the on-site guide Appendix E.

This isn't a dig, but both of you need to familiarise yourself with the whole of appendix 4. Remember also, out of all the appendices, only 1 is normative.

The chances of someone having to apply a grouping factor in your average domestic installation is slim to none.
 
Yes, you do have to de-rate, and also make sure the ducting/trunking is large enough for the cables. If the tables do not show the cables you are using, a 45% 'empty' should suffice - that means the trunking / conduit should not be more than 55% full by volume - or it could be only 45% full, cant remember properly now without going out to get the book out.

It's all in easily readable form in the on-site guide Appendix E.

And applies to single core cables, not double skinned as t+e.
 
Hi,

I have just finished off a kitchen and swapped the CU out at the same time...

Part of the run of the cable goes under the kitchen floor in a duct...

Its 2m long the duct.

When applying rating factors, is there a min and max length in comparison to the overall length of the run?

I have 5 lots of twin and earth running in a duct, strictly speaking I should apply a factor of 0.60 to them but if it was only 2m long does it really need it applying?

0.60? what are these 5 twins which are going to be running at full load 24hours a day in a domestic installation??
 

Reply to Grouping Factors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, Currently 1st fixing new extension however the existing cooker hood duct which was on outside wall will now be part of new utility...
Replies
2
Views
659
hi just bought a new oven its a 4.4KW i`m running a 6mm cable from the cu using a 32mcb to kitchen around a 6M run under floor boards then 2m in...
Replies
9
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
824
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
799
Hi guys I’ve got a motor starter I’ve come across and looking at the electrical drawings it’s originally had 35mm tails from a 100amp fused...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock