Hi guys,

Went to do some garden lights, was going to use the existing cable already feeding the old lights in the garden.
Did R1+R2 and R1+Rn on the feed, figures were roughly 1.2 ohms. The feed was tapped of the downstairs lighting circuit.
I further inspected the accessories, and i noticed the switch feeding the old garden light only had one cable with neutral sleeved as live and live going into common.
I then assumed, that there's obviously a junction box feeding all the downstairs lights, and switched in a similar fashion.

I checked all accessories and they were wired like this.

However, before commencing work, i wanted to just do another test on the feed to the outside garden, i was now getting R1+RN R1+R2 of around 33ohms!

I checked all accessories and they were securely fitted, i checked the db as well.
The homeowner told me there was a massive water leak as well, situated near the lights feeding the outside cable, which i presumed would cause high resistance due to the rust.
But I still can't understand why i got a low reading, then suddenly a high reading.

The downstairs lighting did have a dimmer and i didn't take out the bulbs to eliminate the resistance, but i didn't do that when I got a low reading either.

Does anyone have any ideas?
 
What's R2 +Rn?

If that's still 1.2 ohm, then there is something in circuit R1 - has a switch been operated which previously shorted out a lamp or something
 
I think you have got a little confused with you testing. You mentioned a dimmer, did you test through that switch to get the high reading? Remember as well there is no neutral sleeved red, it's a black, it's only neutral if it is connected to the supply neutral.
The test you need to carry out correctly is R1+R2. With the circuit disconnected connect line and cpc together either at the DB or at the furthest point on the circuit, then carry out a continuity test between line and cpc at the opposite end. If you are on a feed the position of switches will make no difference, if you are at a switched light then that switch will need to be closed or dimmer bypassed. There is no requirement to test R1 or R2 to the N conductor, but if you do so you will need to short out cpc to N at one end and test at the furthest end in the same way.
If any of those readings are high then you will need to break down the circuits to find the fault.
 
What's R2 +Rn?

If that's still 1.2 ohm, then there is something in circuit R1 - has a switch been operated which previously shorted out a lamp or something

I tested both neutral to live and live to earth to check if something is wrong with r1.
R1rn was just a quicker way of typing it.

I'll check your suggestion. Thanks
[automerge]1592590583[/automerge]
I think you have got a little confused with you testing. You mentioned a dimmer, did you test through that switch to get the high reading? Remember as well there is no neutral sleeved red, it's a black, it's only neutral if it is connected to the supply neutral.
The test you need to carry out correctly is R1+R2. With the circuit disconnected connect line and cpc together either at the DB or at the furthest point on the circuit, then carry out a continuity test between line and cpc at the opposite end. If you are on a feed the position of switches will make no difference, if you are at a switched light then that switch will need to be closed or dimmer bypassed. There is no requirement to test R1 or R2 to the N conductor, but if you do so you will need to short out cpc to N at one end and test at the furthest end in the same way.
If any of those readings are high then you will need to break down the circuits to find the fault.


Hi I didn't test at the dimmer, i only mentioned the dimmer because the whole lighting circuit is powered through junction boxes. The switch in question, was wired with one twin-e, the live (red) going into common, and the neutral (black but sleeved in brown) going to L1, and this switched on the old outside lights.

I have tested cpc and live at furthest point and at DB. Still same figures.

When i return, im going to remove the lamps and test it then.
 
Last edited:
I tested both neutral to live and live to earth to check if something is wrong with r1.
R1rn was just a quicker way of typing it.

I'll check your suggestion. Thanks
[automerge]1592590583[/automerge]



Hi I didn't test at the dimmer, i only mentioned the dimmer because the whole lighting circuit is powered through junction boxes. The switch in question, was wired with one twin-e, the live (red) going into common, and the neutral (black but sleeved in brown) going to L1, and this switched on the old outside lights.

I have tested cpc and live at furthest point and at DB. Still same figures.

When i return, im going to remove the lamps and test it then.


R2+Rn is neutral - earth it's the only one which doesn't include line (R1)

Both your previous tests include the line conductor, if this is high resistance it would appear in both your previous tests, but shouldn't appear in the R2+Rn test.
 

Reply to High R1+R2 / R1+RN in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
737
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
213

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock