By measurement. I would check your original result by linking out the rcd, the no-trip test seems to give funny measurements sometimes.
Hi Truckster,
Can you just explain how to link out the RCD please.
Ive never used this method, but I too have sometimes experienced higher Zs results when using the no trip function on my megger 1553.
Thanks for your help,
Sav
 
I do recognise that the readings will change slightly depending on conditions. I also recognise that 15mA will not push through in the same way that a few Amps will. All that said, it is pretty pointless paying all this money for a piece of kit if most of the time the readings are not worth toffee....
I'm hoping it is simply a faulty meter and my faith in Megger can be restored.
 
Well, if you think that the instruments were designed to provide readings using sinewave power signals. The supply waveform has changed but the instrument electronics appear have not.
I think there at least two methods of measurement.
1/ limiting the flow through the instrument to 15mA,
2/ Flooding the magnetic core of the RCD with DC current and then allowing a couple of cycles of something in the region of 10A to flow.

Megger recommend that Zs measurements are done at least three times and the average reading taken.

As far as linking out RCDs while taking Zs readings. This is strongly not advised by all concerned with I&T. However, I used to do it before DLOCK , with a LT5.
 
Last edited:
Hi Truckster,
Can you just explain how to link out the RCD please.
Ive never used this method, but I too have sometimes experienced higher Zs results when using the no trip function on my megger 1553.
Thanks for your help,
Sav

I link from the top of the RCD to the bottom with a couple of short 6mm links. As Ackbarthestar says it's not a recommended method with the advent of d-lock but sometimes it's the only way to get a reading. D-loc doesn't always work and the rcd trips so out come the links.

Do it at your own risk and recognise the dangers from doing so!
 
When I have encountered High readings on a No trip I do it another way.

Isolate the circuit and then link line and earth at the end of the cct or somewhere on the ring if a ring ! (I have a plug made up for this)

At the CU test between the incoming Live and the isolated cct !

Remember to remove your line cpc link prior to switching the cct back on!
 
Thanks for the advice truckster,
I will avoid that may be and just do what Ackbarthestar said, to do the measurement 3 times and take the average.

Im thinking of whether to buy a Fluke, but Im so used to the Megger !!!

Sav

 
I have experienced spurious readings with my MFT 1730 on the L-PE range, and know of two or three other testers who have experienced the same problem. I have made enquiries and Megger have been having issues with their software, hopefully this will be resolved when the instrument is returned for calibration.
I have also had problems with the Metrel MI 3125 on the not trip test where the screen goes blank and then returns to the start screen, i have returned them and the MI3122 RCD / ELI as well, to the manufactures but the problem has reoccurred so this along with the rechargeable batteries not retaining charge during cold weather to do a days testing, I have stopped purchasing the Metrels and reverted back to Megger.
 
Megger 1700 (or 1800) series users might consider of informing 'BBC Watchdog' about this on going saga, it's just sort of case they like to get their teeth into (Toyota stuck accelerator, Ford locking brakes and collapsing suspension) and it might have more effect than the piecemeal electrician's complaints and the platitudes received from Megger?
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How do most of you prefer to do EFLI tests?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
30

Thread Tags

Tags Tags
tests

Advert

Thread statistics

Created
Guitarist,
Last reply from
MarkieSparkie,
Replies
30
Views
6,566

Advert