Went to a ladies house last night, basically she'd been told by an "electrician" that she needed a re-wire. This guy had come in to upgrade her shower to 10mm, and fit a new consumer unit at the same time. He fitted the CU, did a few tests and legged it saying he wasn't going to fit the shower cable 'as her electrics were shot to bits', and he's not Part P registered either, so no LABC notification or installation certificate.
I did a Ze test, got 17.8 ohms(TN-S), and the noticed the clamp with the main earth on the supply cables sheath was hanging off, so I notified DNO straight away.
The ladies sons were present during all this, and obviously not happy campers, and were asking me what can they do about this guy? I don't know so thats why I am asking if any of you guys know what the official line is about reporting these lot doing this type of thing.
Also, can I do an EICR to cover her consumer unit from not having an installation certificate.
Many Thanks