Gravydog

DIY
Reaction score
1
I bought my house new in 1978 with forced air electric heat and in all that time all the maintenance required has been to oil the blower motor a couple of times and I periodically have to replace failed sequencers (time delay relays) when I notice the vent temp is getting low from not all elements being powered. I have a 7.5Kw generator for backup power but my 23Kw furnace has always been beyond reach, of course.

I ordered new sequencers and while waiting for them I studied the schematics. My furnace is fed by 3 separate 240 volt circuits to three internal breakers 60A, 50A and 15A. The 60A fed the transformer, the blower and two 5Kw elements. The 50A fed two more 5Kw elements and the 15A fed the remaining 3Kw element. I wanted to be able to power one 5Kw element with the generator but the 15A breaker was insufficient for that. Luckily, that breaker was fed by a 30A breaker in my service panel over 10 gauge copper wire. I was able to find a 30A replacement breaker for the furnace and installed it.

I rearranged the wiring so that now the new 30A breaker carries the blower, transformer and one 5Kw element while the 60A one has two 5Kw elements on it and the 50A one has one 5Kw plus the 3Kw element. The bottom line is that with the two large breakers turned off the furnace will operate completely normally but with only 5Kw capacity. I tested it out and I was getting at least a 10 degree F. rise in the vent output air compared to the inlet. Winter temperatures here near Seattle seldom dip below the 30s (F) so it could actually work. I think it will be enough to keep the house livable if we have a power outage during cold weather but I hope to never find out! Still, I'm very pleased with myself for doing this modification.

Rob
 

Reply to I rewired my forced air electric furnace to allow partial use on generator in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

M
Aaaargh - attempt 2! I typed loads and the damn computer swallowed it all up :93: I have been asked for some data on my experience with the...
Replies
1
Views
2K
MicraShed
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock