I need to insulate under my suspended floor which has many cables running through the joists (consumer unit is below floor). My main concern is causing the cables to overheat etc. Here's a quick overview:
Joist height: 140mm
Cables: Mixture of circuits but the 2.5mm 32A rings are my main concern (lights etc. would be fine)
Insulation: 2 x 50mm sheeps wool slab (100mm total)
If I do a 50mm slab under the cables then it fits quite snuggly below the cables (just touches but no stress on cables). My thoughts are:
Second slab on top of cables - cables sandwiched between insulation - overheat?
Second slab forced below cables - would probably put stress on the cables (if I can even get it under there)
Put both slabs (100mm) above the cables - this will be compressed around the cables and put some weight on the cables.
Have a gap around the cables with second slab - can I rely on these slabs not moving during the next few decades (probably not)?
Put wood (approx 25mm thick) each side of the cables and lay insulation over the top (leaving a small gap around the cables). This would be hard to do well and the insulation may even rest on the cables
Any ideas how I can do this? I really want to get 100mm insulation as the room does get cold. I don't really like any of my suggestions above but I'm sure others will have had the same problem.
Joist height: 140mm
Cables: Mixture of circuits but the 2.5mm 32A rings are my main concern (lights etc. would be fine)
Insulation: 2 x 50mm sheeps wool slab (100mm total)
If I do a 50mm slab under the cables then it fits quite snuggly below the cables (just touches but no stress on cables). My thoughts are:
Second slab on top of cables - cables sandwiched between insulation - overheat?
Second slab forced below cables - would probably put stress on the cables (if I can even get it under there)
Put both slabs (100mm) above the cables - this will be compressed around the cables and put some weight on the cables.
Have a gap around the cables with second slab - can I rely on these slabs not moving during the next few decades (probably not)?
Put wood (approx 25mm thick) each side of the cables and lay insulation over the top (leaving a small gap around the cables). This would be hard to do well and the insulation may even rest on the cables
Any ideas how I can do this? I really want to get 100mm insulation as the room does get cold. I don't really like any of my suggestions above but I'm sure others will have had the same problem.