Im getting some strange reading on a new circuit(ring main) ive installed and i was wondering if anyone else had experienced the following.

insulation resistance at 500v on L-N is >500mQ (which is fine)
then insulation resistance between N-E starts at 400 then climbs to 500mQ
then insulation resistance L-E starts at 210 then slowly rises to 500mQ with the button held in.

There are no appliances connected and no sockets have been fitted at this point of testing.

Test meter is fluke 1625c (calibrated in november)

Quite bamboozled on this one
surely a damaged cable would get a bad reading and the reading wouldnt climb up to >500MQ eventually?
 
Any damp present?
Did you null the the leads before retesting?
Are there any poor connections, croc clips not making contact properly?
 
those readings are way up in the sky, so why are you concerned. probably breathing on the leads.
 
its an open new build site so you could say maybe some damp.
but its a ring test so ive connected all the points together and then i have the two ends at the boards so i dont know if damp can effect them.

nah i didnt null the leads

think the clips should be fine but i will re-check on that one.

My biggest fear is that somewhere, somehow, when ive been pulling them through joists thats ive got burning on the cables but i did try to take care, not overloading holes etc
 
Delete.
 
Mhmm that video has his earth out of the earth bus bar on IR test.
Well spotted. The 17th Edition prohibited insulation resistance being tested this way.
 
Mhmm that video has his earth out of the earth bus bar on IR test.
Well spotted. The 17th Edition prohibited insulation resistance being tested this way.
 
surely readings climbing are the capacitive effect of wasting batteries on charging up a cable effectively no? And in lore, maybe damp being dried out?
 
  • Agree
Reactions: stevethesparks

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Glasgow

Thread Information

Title
Insulation resistance - strange readings
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
Neon Vagabond,
Last reply from
Old Tiler 43192,
Replies
26
Views
8,337

Advert