Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in the acceptable realms.
 
I assume there is something connected across line and neutral.
 
It's either going to be a load you've haven't disconnected for the test or else there's a fault.
 
I assume there is something connected across line and neutral.
Would that also double with the fact that I’m getting a 99.9ohms reading on resistance testing??
 
Would that also double with the fact that I’m getting a 99.9ohms reading on resistance testing??
A resistance test across line and neutral?
 
Well for practical purposes that's a dead short so you've got a dead short or a lighting fixture still in place. Could also be a neon indicator if you've lights on a neon switch such as outdoors - or a PIR sensor as well.
 
Well for practical purposes that's a dead short so you've got a dead short or a lighting fixture still in place. Could also be a neon indicator if you've lights on a neon switch such as outdoors - or a PIR sensor as well.
Ok I’ll look into it! 👍
 
Well for practical purposes that's a dead short so you've got a dead short or a lighting fixture still in place. Could also be a neon indicator if you've lights on a neon switch such as outdoors - or a PIR sensor as well.
Is it sufficient just to turn the neon FSU off and test? Found one in the loft
 
For what reason are you testing this circuit?
 
it was not long ago that some member put on here about IR testing what you should be looking at if low insulation testing .
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Redditch
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
IPS Culina

Thread Information

Title
Insulation testing problems
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
dunscombe,
Last reply from
buzzlightyear,
Replies
12
Views
1,641

Advert