Nov 19, 2021
Redditch
Business Name
IPS Culina
Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in the acceptable realms.
I assume there is something connected across line and neutral.
It's either going to be a load you've haven't disconnected for the test or else there's a fault.
Would that also double with the fact that I’m getting a 99.9ohms reading on resistance testing??
A resistance test across line and neutral?
Well for practical purposes that's a dead short so you've got a dead short or a lighting fixture still in place. Could also be a neon indicator if you've lights on a neon switch such as outdoors - or a PIR sensor as well.
Ok I’ll look into it! 👍
Is it sufficient just to turn the neon FSU off and test? Found one in the loft
For what reason are you testing this circuit?
it was not long ago that some member put on here about IR testing what you should be looking at if low insulation testing .
Redditch
Business Name
IPS Culina
Insulation testing problems
dunscombe,
buzzlightyear,