Discuss IR Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi All,
Firstly I'll apologise for not trying to collate this with another thread, But thanks to my organisation skills I find myself short on time.
I'm currently at College and coming up to a assignment to do with testing etc. I understand pretty much all area's of testing, However theres a few things that keep popping up and there simple things that could make me fail my test. So could you clear the following up for me.
1) When Doing an individual (i.e. not global) IR test do the MCB's need to be on or off?
2) We have it drilled into us to disconnect RCBO's and every time i do testing I'm now worried that i arent disconnecting them properly, At the moment I just disconnect the L,N and cpc's from the rcbo's, Is that enough or do I need to do anything else?
Any other helpful advice always well appreciated
Thanks in advance
James
you are correct. fo IR testing, you are testing the circuit under test L-N, L-E,N-E. the MCB/RCBO should not be connected to the circuit under test.
Hi mate,
You are IR testing the cables only.
I am assuming single phase here.
Isolate, lock off, post notice, prove dead then,
Disconnect the circuit completely from the dist board, then IR on the cable ends, L-E, L-N, N-E. Job done.
I see no reason to leave it connected to the MCB, and i wouldn't teach anyone to do it like that either. There is no need or purpose in IR testing the breaker.
Three phase do the same with all three phases.
Cheers.........Howard
Thanks for the help guys, It does seem alot easier to disconnect the cables completely, I have always been tought both at work and college to test to the MCB, Hence my question. But I guess removing the cables removes any doubt.
Thanks for your help
Reply to IR Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD Its a 10 way… rammed packed with cabling,,,the...