There are people on here who have been in the trade way longer than I , but I have noticed over my time that pretty much no 2 sparks do a PIR / EICR the same.
I reckon we could send 5 sparks to the same old house and we would get 5 different lot of findings and 5 very different lots of recommendations / Codes
Not sure any would give a board with an RCD main switch a C2, unless it was faulty.
 
Thanks for the advice all, have decided the board will warrant a C3 and have sent a covering email to landlord/agent informing them of the report. I have also let them know that the EICR is not a replacement for an EIC and they may still need to provide this in future. Have quoted to upgrade to RCBO/SPD but I'm not holding out much hope looking at the rest of the flat!
 
This doesn’t warrant a C2

Going by your logic most consumer units I test I’d have to give a C2 as most aren’t full RCBO with SPD
With respect, I never said it would be a C2 purely based on it having a single RCD, but because it had a single RCD installed recently. I accept that I was wrong with this, and that the age of installation is irrelevant, but I still maintain it shouldn't have been installed that way.
If you C2 all RCD boards then dual RCD boards will be C2 as well , which as you say we would be C2ing a lot of fairly new builds
Not at all, my point was that a single RCD is no longer compliant. A dual RCD is still compliant so it wouldn't warrant any kind of remark at all. Not that I like fitting them anymore when RCBOs are so much better.
 
With respect, I never said it would be a C2 purely based on it having a single RCD, but because it had a single RCD installed recently. I accept that I was wrong with this, and that the age of installation is irrelevant, but I still maintain it shouldn't have been installed that way.

Not at all, my point was that a single RCD is no longer compliant. A dual RCD is still compliant so it wouldn't warrant any kind of remark at all. Not that I like fitting them anymore when RCBOs are so much better.
Remind me again why it's not compliant and is that a statutory reg??
 
Remind me again why it's not compliant and is that a statutory reg??
BS7671 314.1 and 531.3.2

None of BS7671 is statutory but it is still what we are required to follow - are you suggesting it's compliant right now to fit a single RCD consumer unit feeding one house/flat? Happy to be proved wrong but I'm fairly sure that's not the case?
 
BS7671 314.1 and 531.3.2

None of BS7671 is statutory but it is still what we are required to follow - are you suggesting it's compliant right now to fit a single RCD consumer unit feeding one house/flat? Happy to be proved wrong but I'm fairly sure that's not the case?
Not sure 314.1 says not to use them or 531.3.2. Can you be more specific.
 
BS7671 314.1 and 531.3.2

None of BS7671 is statutory but it is still what we are required to follow - are you suggesting it's compliant right now to fit a single RCD consumer unit feeding one house/flat? Happy to be proved wrong but I'm fairly sure that's not the case?
Remember in the new edition to be aware of the words should & shall.
 
There are no should's in the regs I quoted, only shalls...
Your right on both counts but your still wrong with your classification of the fault and nowhere does it say not to use them. In the right application they're fine. Unless your going to go round the tenants property and workout the earth leakage from all their appliances but even then it would be a C3 as it's only a nuisance. In other areas a board with an RCD main switch is the right choice. On an EICR we can put notes along with our classifications which should be done in a case like this. Yes they are all shalls as in divide circuits & minimise hazards but it still leaves it open so we can choose the best protective devices for what we are installing and at the time that was the best way so it's still a C3 with advice. RCD main switches are fine if that's what's required.
 
Your right on both counts but your still wrong with your classification of the fault and nowhere does it say not to use them. In the right application they're fine. Unless your going to go round the tenants property and workout the earth leakage from all their appliances but even then it would be a C3 as it's only a nuisance. In other areas a board with an RCD main switch is the right choice. On an EICR we can put notes along with our classifications which should be done in a case like this. Yes they are all shalls as in divide circuits & minimise hazards but it still leaves it open so we can choose the best protective devices for what we are installing and at the time that was the best way so it's still a C3 with advice. RCD main switches are fine if that's what's required.
I don't think you've fully read my posts. I now accept that it is a code 3, and under normal circumstances that is absolutely what I would code a single RCD board. The reason I thought this one might be considered different is because it is clearly a new board (amendment 3 compliant) and therefore was installed at a time when Split Load was required at a minimum in this kind of installation. You say 'at the time this was the best way', but in this instance it definitely wasn't.
 
Unless your going to go round the tenants property and workout the earth leakage from all their appliances but even then it would be a C3 as it's only a nuisance.

Measuring earth leakage is not relevant, that is only relevant to actual unwanted tripping, we are not concerned with that, we are concerned with limiting the risk of unwanted tripping.
Regardless of what the actual earth leakage is at any one time there is always a risk of unwanted tripping due to it changing.

Yes it is a C3, but that just proves that it is not compliant!
C3 is given to items which do not comply, do not present a potential or immediate danger, but can be improved for safety.

A C3 is not given to things which comply!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sussex, UK

Thread Information

Title
Landlord's EICR query
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
42

Thread Tags

Tags Tags
eicr query

Advert

Thread statistics

Created
frontier219,
Last reply from
davesparks,
Replies
42
Views
5,900

Advert

Back
Top