Hi All,
WIth new reg is it a true that the every lighting circuit have to be protected by rcd ?
I agree with you. But what about industrial and comercial premises ?411.3.4 Within domestic premises additional protection by RCD not exceeding 30mA shall be provided for AC final circuits supplying luminaires.
Not the exact wording but near enough.
does not apply.I agree with you. But what about industrial and comercial premises ?
There is no blanket statement like domestic for commercial and industrial lighting circuits however the installation method of the circuit may result in the requirement.I agree with you. But what about industrial and comercial premises ?
This would be down to the installation method and if there's any requirements for compliance with certain areas of Part 7.I agree with you. But what about industrial and comercial premises ?
If lighting circuit is all surface, pvc conduit/pvc trunking/ surface/ clipped direct .
IMO that would omit the rcd requirement.
Tin hat on , good debate eh. (new installs)