Lounge lights not working.
No RCD tripping.
No MCB tripping.
Lights wired power-switch-light. New switch and pendant installed.
Meggar test shows following voltages when switch is off.
L-N 235V
L-E 235V
N-E 18V

When light is switched on,
L-N 235V
L-E 235V
N-E 175V

Is someone able to give some advice as to why I may be getting these readings. Continuity and polarity tests fine.
Lights still not working.
Thanks in advance.
 
...Continuity and polarity tests fine....
What are your actual R1, Rn and R2 readings at the light with the switch closed? (or R1+R2 and R1+Rn)
 
sounds like a floating neutral, poor connection.
 
What are your actual R1, Rn and R2 readings at the light with the switch closed? (or R1+R2 and R1+Rn)
Dont think the OP is a Spark HS
 
Dont think the OP is a Spark HS

Not sure I agree with that, the op states continuity and polarity good

Edit : having read a couple of previous threads I don’t think he is, nor does he appreciate and questions about ability .......he just expects answers on a plate
 
Last edited by a moderator:
  • Like
Reactions: Baker1988
Not sure I agree with that, the op states continuity and polarity good

Edit : having read a couple of previous threads I don’t think he is, nor does he appreciate and questions about ability .......he just expects answers on a plate
Glad you agree with me.
 
  • Funny
Reactions: 1 person
Meggar test shows following voltages when switch is off.
L-N 235V
L-E 235V
N-E 18V

When light is switched on,
L-N 235V
L-E 235V
N-E 175V

‘Megger test’ is the common term for an insulation resistance test, but your test results imply that you’ve measured the voltage. Can you clarify what you mean here?
 
Have the lights stopped working after the new switch and pendant were installed? Or were these installed due to the fault, in the hope they might fix it?
 
  • Optimistic
Reactions: 1 person
more info is needed here, what location are you testing from?
what is the total length of the circuit from the ring or radial to the lamp?
the original post lends a lot of questions on the qualifications hence the reason for asking if the OP is a spark
 
  • Agree
Reactions: Pete999
  • Like
  • Funny
Reactions: Baddegg and Pete999
He can't be a spark as he'd know that with the switch off, L-N would be 0V not 235V.

With the switch on N-E is giving 175V. I've had similar in the past where the N was an unsleeved L and the client in replacing the pendant had got everything mixed up so when the switch was on the switched L was going through this light and the next light in series.

He needs a professional with test gear and more importantly knowledge to get it sorted out safely.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Lounge light neutral problem
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
Martin606,
Last reply from
Adam W,
Replies
12
Views
2,101

Advert