Having to re cable the lighting in a metal portacabin,the cabin is placed in a workshop,would you main bond it,doubts due to new 18 th edition,on the requirements of main bonding.
The cabin is not an extraneous conductive part,& will be earthed fortuitously by the lighting equipment.
 
Having to re cable the lighting in a metal portacabin,the cabin is placed in a workshop,would you main bond it,doubts due to new 18 th edition,on the requirements of main bonding.
The cabin is not an extraneous conductive part,& will be earthed fortuitously by the lighting equipment.
What with a Crabby 1mm2 cpc, cosmic
 
  • Funny
Reactions: suffolkspark
Yea,don’t seem right does it,before the 18th,definite main bond with appropriate cable.
 
The requirements as to whether the cabin needs bonding are no different from the 17th Ed to the 18th Ed. Nothing has changed.
 
  • Agree
Reactions: Risteard
Does it need bonding.
 
Im looking @ it,with these new regs,on bonding,it states that if it’s a plastic insert,on incoming pipes,then no bonding required.
This includes all other pipework that is relevant to that system,it does not need bonding.
With that in mind,the Cabin isn’t extraneous & so does not require main bonding,but earthed locally by cpc of the equipment inside.
 
I doubt it requires protective bonding unless the cabin has its foundations anchored or bolted through the flooring membrane and in good contact with the general mass of earth below.
 
  • Agree
Reactions: Richard Burns
I doubt it requires protective bonding unless the cabin has its foundations anchored or bolted through the flooring membrane and in good contact with the general mass of earth below.
Cheers
 
Yes I stand corrected I shouldnt have said that, it is meant to be an unbroken run from met.
 
The Swa supplying the DB not sized appropriately to allow main bonding.
 
  • Disagree
Reactions: Pete999
It can’t be an extraneous conductive part,cause it’s inside the building.
Why bond it when there’s no need to bond metal pipes in situ,if they have a plastic insert @ entry to that building .
 
Why bond it if you’ve said it’s not extraneous??
Agrre but what tests have been done to prove it's not extraneous?
 
It can’t be an extraneous conductive part,cause it’s inside the building.
Why bond it when there’s no need to bond metal pipes in situ,if they have a plastic insert @ entry to that building .
You could say that about any metalwork within the building that may or may not be classed as extraneous.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Main bonding to do or not to do
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
cliffed,
Last reply from
Deleted member 26818,
Replies
29
Views
4,701

Advert