Discuss Main earth size on TN-S in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
Hi guys.
I was on EICR yesterday, where i found that the main earthing conductor is with very small csa- no more than 2.5cm2.
Also they run the wire directly behind the CU, where it is twisted with 10mm2 and continues to the MET inside the board.
Ze at the board is 0.28 ohms and seems to be ok, but the size worries me.
How would you code that and whose responsibility is to replace that wire?
Thanks.326676185_486876280294096_6197944382010337205_n.jpg326558252_5914616958602878_6602939282741313154_n.jpg326558252_5914616958602878_6602939282741313154_n.jpg326676185_486876280294096_6197944382010337205_n.jpg
 

Attachments

  • 326410170_487176616708686_5780506417452227453_n.jpg
    539.8 KB · Views: 10
If, as it appears to be, a TN earthing arrangement then it would be C2 for "Cross-sectional area of the earthing conductor does not satisfy adiabatic requirements (that is, does not comply with Regulation 543.1.1)" from latest BPG#4

The connection to the incoming cable would be the DNO's responsibility, but there is also the chance they decline to provide an earth and you have to TT the installation as a result. That would obviously have major implications for the extent of RCD protection.
 
Not until you have actually done the calculation though!
True...but min CPC for even the low-end assumption 63A fuse at that sort of Zs is 4mm and its not looking to meet that!

Edits:
A quick check is to look in the OSG Table B3/B4/B5 and see if it meets/exceeds the acceptable CPC for a given supply fuse and Zs.

Also not clear if PME condition exist or not, if so then it is going to fail on the 10mm minimum (reg 542.3.1 that cites 544.1.1 for that)

Also 543.1.1 also has a minimum of 2.5mm and I strongly suspect it fails on that as well, but come callipers and calculation would be needed to verify it.
 
Last edited:
Not sure if you can calculate for the Main Earth Conductor
My first visual check was it looked like two strands of 30A fuse wire!

My own starting point is you should be able to clear the DNO fuse worst case, hence the starting point of looking at the OSG tables for the fuse CPC versus Zs values that meet the adiabatic. But ultimately if should be at least 6mm on old systems and really ought to be 16mm these days based on the 16mm/25mm sort of supply cable.

Even if you were looking at final circuit clearing, it would have to be something like the CPC size of the heaviest circuit to be acceptable, so again typically 2.5mm to 6mm or so on that optimistic case.
 

Reply to Main earth size on TN-S in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
770
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
664
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock