Hi guys got a assessment coming up this monday. Got a new meter as above, but didnt come with Fused test leads, i practiced without these, and know how to use the instrument well....

I purchased the fused test leads on monday, and have done 2 Ze tests on 2 differant properties with my boss, and each time the fuse blows in the Line probe.

Im doing a Ze test as per instructions in manual, select Loop L-E, discon main earth croc clip to earth, N probe then Line Probe, press start and and get rcd message..... go to do it again, says no voltage...
I then test my fuses out the probes and the line probe fuse has blown....

I just read on here on another thread that my tester can aslo do Ze by linking up E-N probes together and clip it to earth, and put probe on line..... Well done this and got the same outcome.....

Has anyone else had this problem, i get the feeling im screwed for monday now!!!!

Cheers guys
 
Last edited by a moderator:
Don't use fused leads for Ze or Zs as the fuses in the leads are only about 500mA.

When conducting these tests your meter puts out a current of about 25A therfore blowing the fuses.
 
so basically all that im doing is right, what about the regs about using fused test leads, is this just another contridiction that made up to make the book bigger LOL:)
 
But your instrument and probes should be GS38 compliant therefore your require suitable finger guards, 4mm maximum tips and fused probes
 
Should not be a problem not using fused leads i had my assessment last week using the same meter just piggy back earth and neutral leads to disconnected main earth and line lead to live terminal.
 
cheers robskiing.... I will mention this to my assessor before we get started and see what he has to say.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Metrel 61557 Instaltest
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Thread Tags

Tags Tags
metrel

Advert

Thread statistics

Created
danny124,
Last reply from
danny124,
Replies
6
Views
4,127

Advert