Good evening gents.

Thanks for the helpful advice where given. Warm and dry now. Sorry for the lack of info. It was motorway spec cable. 150Ohms/L is the minimum. Was not thinking straight due to the frost bite setting in but knew it was there abouts.

Think sometimes to often when a question is asked on here the answer is look at the regs. Sometimes you need a little help in a shtt situation.

Cheers

Hi bud,this would have been easier,if we knew the situation and type of cable.

Where has the "1500hms/L" come from? :smiley2: ...or "150 Ohms/L" even?
 
Last edited:
The original question asked what the minimum IR value for a 230v cable is as a regs book wasn't to hand, that implies the OP required the minimum value stated in bs 7671...which is 1 megohm!

It's no longer clear exactly what the OP was asking but there's an important difference between the minimum acceptable IR for 70mm² cable and the IR for a circuit using that cable. 1 metre of 70mm² would be considered faulty and rejected if it could only achieve 1MΩ, but wire it between a fuse-switch and a busbar chamber and test it on a damp day and 1MΩ might be realistic. OTOH a 600m run of cable might not be so bad at 1MΩ so when you are looking at larger cables and longer runs you can't just say 1MΩ is the limit and that's that.

Hence the figure in MΩ.km (sometimes misquoted as MΩ/km which is a nonsense) that manufacturers give for each size and type of cable, or they refer to the one in the BS for that cable. If the '150 ohms/l' is supposed to say megohms then it makes sense to me.
 
Spanner in the works. 1500 Ohms or 1.5MOhms is the minimum per kilometer / by the Length is the minimum for motorway spec power cable. Typo after one of those days where you are glad to put behind you. Thanks all the same.
 
Last edited by a moderator:

Reply to Minimum IR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm either going mad or blind, but I went looking in the brown book the other day to find the small bit where it gives minimum support spacings...
Replies
5
Views
356
What are the minimum testing tools every electricition is required to have in their tool box ? And a is a multificunctional tester a necessarity?
Replies
36
Views
2K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
699
I have an new set of circs here... Landlord in Cyprus EICR needed in empty flat. No credit on meter. Need power for Ze (TNCS) and RCD test at...
Replies
11
Views
467
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock