If you take the earth leakage fault, things to consider:
1) The 50Hz ac waveform has a period of 20ms for one cycle. Assuming a simple resistive leakage, and starting with the mains waveform at 0V, it has to rise to a high enough voltage to reach the leakage trip current - if nearing peak voltage that would take 5mS. If the RCBO has been designed to ignore transients, it might want to look at the decending voltage trigger point too, or the -ve half of the cycle as well to do another measurement. If the latter we are talking about at least 15mS, getting on for a full cycle of 20mS. Of course the 'fault' may occur at any point during the cycle, but it's random chance when. Just trying to point out there are physical reasons why you cannot guarantee 'instant'.
2) The 30mA 40mS trip 'standard' has been determined to be safe, so in principle there's no advantage to quicker trip times, unless there is some technical requirement.
3) You could choose a lower trip limit for the leakage current, which by implication would cause a quicker trip. There are fancy earth leakage breakers where you can set trip current, here's an example of one starting at 6mA:
There are no doubt other special purpose safety devices on the market that might do what you want, but understanding what it is you want to achieve by having a faster trip, would help